    Goodman Packaged unit-NO fan, NO heat, NO cooling
    :confused: I have a goodman packaged, forced air, 3 ton, 208/230v outside unit. I believe it's about 4 years old and 92,000 BTU. The problem started with getting only cool air no matter what it was set on and the fan worked fine. I replaced the thermostat with a honeywell programmable. I have 6 wires coming out the wall to the stat. I connected the yellow and the green to the stats 'y and g'. Connected the white wire to the stats 'w'. Then the red to the stats 'rh' which was jumped to the stats 'rc'. I taped off the brown and blue. After everything was set and turned on-there was nothing. With the fan in either on or auto it would not come on. No matter what the setting there was no cool air or no heat. With everything double checked including the circuit breaker nothing worked. I tried removing the jumper from rh to rc and had the red wire connected to only the rh. Still nothing. I manually tripped the breaker to the goodman unit, which is 30 amp, and reset it. It appears to be fine as it always stays on. The problem would seem to be a simple one but one I'm not seeing. I'm assuming it's something within the ac/heating unit itself but have no idea. I really appreciate any response as it's getting hard to stay warm with just these small portable heaters. I thank you very much for any and all responses... mankinddad
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Dec 3, 2007, 07:11 PM
    Model number and brand of thermostat you are working with.
    MANKINDDAD's Avatar
    MANKINDDAD Posts: 4, Reputation: 1
    New Member
     
    #3

    Dec 3, 2007, 08:09 PM
    To hvac1000;
    The thermostat is a honeywell model rth221 b1000... [email protected]
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Dec 3, 2007, 09:02 PM
    Sounds to me like the reversing valves are staying in the cooling mode. Does the system have a diagram showing if the valves are energized for heating or cooling? The thermostat must be wired or programed right. The valves must work.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Dec 3, 2007, 10:56 PM
    If your unit is a heat pump the thermostat will not work. Here is the diagram for your thermostat.

    http://customer.honeywell.com/techli...69-2060EFS.pdf
    MANKINDDAD's Avatar
    MANKINDDAD Posts: 4, Reputation: 1
    New Member
     
    #6

    Dec 4, 2007, 12:38 AM
    Many thanks for the help to hvac1000 and labman. Specifically though for hvac1000- I'm assuming now that I must have a heat pump. Being somewhat ignorant in this matter, I admit I really don't know what the difference would be with a heat pump. I read that a heat pump sits on legs but thought that any unit that size would sit on legs or something. Is there a way of knowing for sure if it is a heat pump. I have no literature for the unit. It came with the house when I bought the house. Without going to any more trouble do you know what model thermostat I would now buy for the goodman unit. The model # is pgb036100-1b. When I looked this number up I could not find it for any goodman product.
    If however this is the answer to my problem, I am truly indebted, as this would save me much time and money. Thanks much... [email protected]
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Dec 4, 2007, 04:10 AM
    WOOPS I might have misled you.According to the info below yours is not a heat pump. See here

    http://www.alpinehomeair.com/related...010%20SEER.pdf

    http://site.famousparts.com/goodman/IO-148.pdf
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #8

    Dec 4, 2007, 05:12 AM
    It is common enough not to be sure if you have a heat pump, that the sticky at https://www.askmehelpdesk.com/heatin...ons-58313.html
    Has a section on it.

    We really need to know just what you have to help. Your original post sounded like a heat pump. If it isn't, go to the furnace and make sure the wires you connected are connected to the proper terminals there. See if the blue and brown are connected to anything. Most furnace/A/C units need a 4 wire cable. Often there are unused wires. The cable should go into the furnace or air handler near where the filters are. Have you ever changed them?
    MANKINDDAD's Avatar
    MANKINDDAD Posts: 4, Reputation: 1
    New Member
     
    #9

    Dec 5, 2007, 12:57 PM
    I finally got this running okay. Turns out it's a gas pack (packaged) unit. I replaced the fuse inside the unit which really didn't look too bad, turned the elec. Power back on as well as the stats heat setting. It tried to ignite over and over but never made it until, I believe it's called a rollout switch or button, was pressed, resetting it and it operated fine ever since. This entire
    'project' has been a good learning experience for me and I thank you guys, labman and hvac1000. Till our paths meet again... mankinddad

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

New ac with heat strip blows out cool air. [ 5 Answers ]

I recently (8 months)had a Fedders Ac System installed with a heat strip, but the heat does not seem to work properly. It blows out cool air and takes for ever to warm the house. The contractor has since moved to Dubai so I cannot get in touch with him. Is there anything I can check myself ?...

GE Furnace Won't Heat OR Cool [ 2 Answers ]

Good Morning, We live in Fayetteville, NC and it's starting to get cold. General Electric Gas Pack model number BLD055E936B1 manufactured in the early eighties has decided to quit. It is a forced air model with a standing pilot. Pilot works great... but the main burners won't light. This has...

Heat, but no cool [ 4 Answers ]

I replaced a old round thermostat with a programmable thermostat. I have two sets of wires coming out of the wall. One single red wire, and a group of wires that are red, white, yellow, and green. I connected them according to the instructions, but obviously that was not right. The single red...

Furnace will not switch from heat to cool [ 2 Answers ]

My furnace operates fine, until I switch from heat to cool. When I switch it willnot do anythig and I have to call out a reapirman. My house was under warranty and I thought the problem was resolved, but it wasn't . What are some thins I can look at?

My Heater Will Heat then Cool? [ 4 Answers ]

The central heating and air unit we have is approximately 2 years old. In the summertime, the AC operates properly. However, in the winter months, the heating unit seems to be malfunctioning. We will set the thermostat to a certain temperature and the heater will heat the house to the set...