    Gfi with switch
    I want to replace my bathroom receptacle with switch (for overhead lite) with a gfi w/switch. My source hot line comes in with a 2 wire line (black/white). The line in the wall has a 3 wire line (black/white/red). What is the proper way to wire the line side of the gfi and the load side? I want the receptacle to be hot when the lite swich is in the off position.
    Thanks
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Dec 1, 2005, 07:11 AM
    Where does this 3 wire cable go and what are the functions of the black and red wire? Does it feed other receptacles or is it a 3 way light switch? Power to the light or switch would connect to the black feed wire as well as the line terminal of the GFI. Any feed through GFI outlets would connect to the load terminal of the GFI outlet.
    aschel's Avatar
    aschel Posts: 8, Reputation: 1
    New Member
     
    #3

    Dec 1, 2005, 10:19 AM
    Quote Originally Posted by labman
    Where does this 3 wire cable go and what are the functions of the black and red wire? Does it feed other receptacles or is it a 3 way light switch? Power to the light or switch would connect to the black feed wire as well as the line terminal of the GFI. Any feed through GFI outlets would connect to the load terminal of the GFI outlet.
    The black and red feed other receptacles-not a 3 way.
    When I look at the gfi w/switch I see on the lower part where it says "line" and has 2 push-in holes on the brass side and 2 on the silver side. What do I connect there?
    Above that I see "load" which has 1 screw connection on each the brass and silver side. What do I connect there?

    Thanks
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Dec 1, 2005, 02:38 PM
    Connect the incoming black to the brass line side of the GFI. Anything you connect to the brass load terminals will be GFI protected too. Anything you don't want the GFI protection, connect to the other line terminal. I the switch doesn't have a built in jumper, it will also need to be connected to the line brass terminal.
    aschel's Avatar
    aschel Posts: 8, Reputation: 1
    New Member
     
    #5

    Dec 11, 2005, 07:36 AM
    O.K. I've got that so far but now I see that the receptacle has 2 black leads coming out of it above the load connections which are marked "switch leads". I assume 1 would go to the brass load but where does the other go?
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #6

    Dec 11, 2005, 11:50 AM
    If the light is over the tub or shower, it needs to be GFI too. Check the 2 leads and brass load terminal with a test light or ohmmeter and I think they all 3 will be connected. To make the light GFI, connect one of them to one of the switch terminals. Cap the other. You may want to check this against any directions that came with the device.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Networking Switch 2 Switch [ 2 Answers ]

I have 2 buildings I want to network together. They are currently being linked by 2 hubs but I would like to replace them with switches. Is there any known performance issues with linking switches together. (e.g. Bandwidth is less on the uplinked switch) I think I already know the answer but I'd...

New switch [ 2 Answers ]

HELP I've been to both Lowe's and home depot and no help yet. I'm installing a new switch and two new outlets both outlets to be energized at the same time. I've run three new 14/2 wires into the attic and joined them in a junction box I ran a new wire into an existing hot outlet which has two...

Switch question [ 15 Answers ]

Hi, I have been looking for hours and still could not find a switch I want. I need a Slide Switch, BUT instead of when you switch it it clicks, I want it to gradually (slide) move. Let’s make this simple and let’s say I have 2 motors and a battery. I want the battery wired in the middle and...

Limit Switch - Pressure Switch [ 0 Answers ]

Hello Folks, This weekend I've been playing with a heating system at my new apartment and I'm trying to figure out what the different componets do. I kind of followed the circuit but still have some missing links... 1-There are some terminals on the furnace's circuit board labeled LIMIT. The...

How do I switch from MS-DOS to WIN '98 [ 3 Answers ]

Hello: I recently chose MS-DOS option when starting my IBM laptop (has Windows '98), and do not seem to be able to go back to Windows 98 view? Each time I turn my laptop on, I keep getting the c:/windows/ line, and I have no idea what I need to type in? Please help! Thanks a bunch! Tio


View more questions Search