    Electrical Main Entrance Panel Move
    I'm renovating and will have to move my main electrical entrance 5 feet from 1st floor to
    Basement.
    1. I know my service entrance will have to move with a longer feed from the pole
    2. Is there a junction box available for ~10 circuits to be extended from
    The old location to the new location? Otherwise; it could require rewiring...
    3. Is it code legal to sheet rock over this junction box eliminating access?
    4. If not #3; is it code legal to install this junction box on the outside wall?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 23, 2007, 05:52 AM
    My answers and comments follow your questions:

    1. I know my service entrance will have to move with a longer feed from the pole.

    So, are you just relocating the panel? If the panel will be farther with a longer feeder from the meter, the meter may need to have a Main Disconnect located at the meter also. A panel that contains the main breaker must be as close to the entrance to the building as possible. There is a unwritten general rule that allows for 10 feet of feeder cable allowed for point of entry to the main breaker.

    The issue is the feeder cable before a Main Breaker is considered as unprotected, any short will not trip any fuse or breaker, as there are none. So caution is needed to keep this cable as short as possible.

    From the Main Breaker, 4 wire cable must be used to feed any panel. The neutral and equipment ground become separated beyond the Main.

    2. Is there a junction box available for ~10 circuits to be extended from
    the old location to the new location? Otherwise; it could require rewiring...

    There are junction boxes of any size available. For 10 circuits, a 12" x 12" x 6" should be just the right size.

    3. Is it code legal to sheet rock over this junction box eliminating access?

    No, it is never allowed to bury a junction box. The cover must always be accessible.

    4. If not #3; is it code legal to install this junction box on the outside wall?

    Sure, a JB can be mounted on an exterior wall. If inside, it can be a standard box, called NEMA 1. If the box will be outside exposed to the weather, then the box will need to be raintight, called either NEMA 3R or NEMA 4.
    boaski75's Avatar
    boaski75 Posts: 3, Reputation: 1
    New Member
     
    #3

    Nov 26, 2007, 06:02 PM
    Quote Originally Posted by boaski75
    I'm renovating and will have to move my main electrical entrance 5 feet from 1st floor to
    basement.
    1. I know my service entrance will have to move with a longer feed from the pole
    2. Is there a junction box available for ~10 circuits to be extended from
    the old location to the new location? Otherwise; it could require rewiring...
    3. Is it code legal to sheet rock over this junction box eliminating access?
    4. If not #3; is it code legal to install this junction box on the outside wall?
    tkrussell;

    Thanks for your quick response and recommendations
    boaski75's Avatar
    boaski75 Posts: 3, Reputation: 1
    New Member
     
    #4

    Nov 26, 2007, 06:04 PM
    Comment on tkrussell's post
    Most helpful

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Difference between Main Lug and Main Breaker Panel [ 8 Answers ]

What is the difference between a Main Breaker Panel and a Main Lug Panel and can either be used in new residential construction.

Breaker size in main panel to support sub panel? [ 7 Answers ]

Hello, I am wiring a sub-panel to the outside of my home (50 feet from main 200 amp box). I ran 3 wire - 6 gauge. What is the largest 2 pole breaker I can put in the main panel to supply the sub-panel. TYPE NM-B 6-3 WITH GROUND 600 VOLTS CIRTEX-I EZ-STRIP (R) PLUS 17:11 2/5/07 SB/RC ...

Main Circuit Panel to Branch Panel? [ 1 Answers ]

Hello experts, OK... My Main Load center in my home has a branch circuit connected to a 60 amp breaker. The branch feed wire is a 4awg copper wire. The branch panel is downstairs and it has a 100amp main cutoff breaker installed in it. It feeds the whole downstairs including... (1)...

Main Electrical Panel [ 1 Answers ]

We want to add a deck off our master bedroom. The main electrical box/outside will have to be away from the house it will be in the way. There is no where to move it on the back of our house, too many windows and doors. Were can we move it? How far? Can we attach to a pole, garage, or a shed? We...

Moving Main Electrical Panel [ 1 Answers ]

Hello All You Very Helpful People I Am Wanting To Move My Main Electrical Panel Literally Around A Corner Less Than 1' Away Any Suggestions? Thanks Marianne


View more questions Search