    lyncha00's Avatar
    lyncha00 Posts: 2, Reputation: 1
    New Member
     
    #1

    Nov 19, 2007, 08:17 AM
    Tempstar blower doesn't come on
    Having problems with my Tempstar furnace, the blower fails to come on automatically when the oil burner starts up but can be turned on manually from the thermostat. I think the problem is intermittent.

    Took a look at the blower, the windings were covered in 1/2 inch of dust but the fan itself looked OK and spins freely. I oiled the bearings and vacuumed out the windings and it seemed to fix it for a 1/2 day but then failed this morning. Could this be a capacitor or relay issue? Thanks in advance for any help.

    The model # is NLOD084FF01, style # NLO84AF.
    tsa7man's Avatar
    tsa7man Posts: 154, Reputation: 9
    Junior Member
     
    #2

    Nov 19, 2007, 08:38 AM
    Check your capacitor with a meter, it could be bad, or weak, it should test to being close to the farrad rating marked on it... or with the heavy dust in the cooling ports of the motor you could have over heated the windings and damaged the motor, but the capacitor is the first thing to check and the cheapest to replace... if you don't have the proper meter to check it, take the cap to a HVAC parts store and get a replacement, and NOTE: don't touch the two ends until you short the two terminals together with a insulated screwdriver, to discharge the stored electrical charge!
    lyncha00's Avatar
    lyncha00 Posts: 2, Reputation: 1
    New Member
     
    #3

    Nov 20, 2007, 10:19 AM
    Quote Originally Posted by tsa7man
    Check your capacitor with a meter, it could be bad, or weak, it should test to being close to the farrad rating marked on it..... or with the heavy dust in the cooling ports of the motor you could have over heated the windings and damaged the motor, but the capacitor is the first thing to check and the cheapest to replace....if you don't have the proper meter to check it, take the cap to a HVAC parts store and get a replacement, and NOTE: don't touch the two ends until you short the two terminals together with a insulated screwdriver, to discharge the stored electrical charge !!

    I tried a new capacitor, same problem still happening. Thinking maybe the honeywell fan limit control? Are these known for getting dirty or going bad?
    tsa7man's Avatar
    tsa7man Posts: 154, Reputation: 9
    Junior Member
     
    #4

    Nov 20, 2007, 07:35 PM
    You may be correct, I'll look up that part number Wed. am and post that for you...

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Tempstar Furnace [ 2 Answers ]

I have a gas Tempstar furnace , The pilot ignites but the furnace does not it tries a few times then stops. The blower works . What might the problem be?

Tempstar furnace [ 6 Answers ]

I have an 80+ tempstar with the smartvalve gas valve. During the call for heat, the inducer motor starts, but the ignitor will not come on and light. I checked the ignitor and it is good. I checked for voltage and it is good. Could the gas valve be bad, since the ignitor is controlled by the valve...

Tempstar experts? [ 2 Answers ]

Blower stay on even thermostat is disconnected at the board. Replace board but it's still doing the same thing.

Tempstar 5000 [ 1 Answers ]

I have a Tempstar 5000 A/C unit and would like to know the condenser size It's model # is ca5536uka1 so should I assume it is a 3 ton unit? Thanks Erik

Tempstar 5000 [ 3 Answers ]

I have changed the coil because it looks like it had a spark or got hot because there was black soot on the power terminals so I replaced it but it still doesn't work. When you turn it on there is a small hum the magnets are not being pulled in, when you push them in humming gets louder from the...


View more questions Search