    #1

    Sep 24, 2007, 04:08 PM
    Installing second service panel
    QUESTION: I am finishing off my basement and would like to add a service panel box in the basement. I have a 200amp panel box in my garage with 11 open slots out of 32. The builder pre wired a wire from the panel to the basement. The wire has a orange shield with #10 wire. There are 4 wires (3 and a ground). I would like to add a second service panel in the basement using the pre installed wire. My question is what size breaker should I use in the garage to go to my new service panel in the basement? I plan on adding a small service panel with 8 to 10 blanks. The will be for lights, outlets and baseboard heating units.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Sep 25, 2007, 02:38 AM
    With the provided #10 wire, all you can connect is a 30 amp breaker, which may not be enough for what you plan on having in the basement, esp considering the electric heat. The 30 amp breaker/circuit may be just enough for the heat alone.
    You will need to run a new larger cable, either #8 for 40 amp or #6 for a 50 amp subpanel, depending on the proposed load in the basement.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Service Panel - Access [ 7 Answers ]

Is there any way to install finish trim around the basement service panel? I'm refinishing a basement bedroom with wallboard. Along one wall are two closets with that gray service panel between them. What kind of access to the service panel is required and does anyone have any suggestions for...

200 AMP Service panel to 200Amp Sub Panel [ 1 Answers ]

I getting new 200Amp service to surface mount service panel. I want to run 2oo cable to bring it sub panel in my Garage which is approx 120Ft Run through ceiling. 2 Questions 1. Is there any ristriction on running a 200AMP inside house to garage ? 2. I got a dirt cheap subpanel that has...

Wire at the service panel [ 1 Answers ]

I am installing a GEŽ 30" Free-Standing Electric Range(JBS55WK/CK/BK). It can use a 3 or 4-WIRE CONDUIT INSTALLATION plug from the range to the outlet. I have a double braker space available at the service panel. I have installed brakers into the panel for outlets and lights and then had them...

Main Service Panel needs [ 9 Answers ]

I ran across this site accidentally today and found someone who had many of the same issues I need help with. Most of my questions were answered reading the forum however I have one more, using the following information I am hoping someone can help. The existing house is apx. 2300 sq ft w/a 200...


View more questions Search