    Gravity furnace gas valve
    Have an old gravity furnace. Pilot generator putting out 575 mv, however gas valve won't open (ITT General Controls B60 gas valve).

    How do I troubleshoot valve? What external or internal checks? I have the valve head off and looking under the diaphragm I don't see anything obvious.

    I'm not sure how it works... when the 575 mv is applied it opens the small vent tube to relieve pressure on the back of the diaphragm?? The incoming gas pressure can then lift the very light spring pressure holding the diaphragm down? What should I be looking for?

    Thanks!

    Derek
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Oct 12, 2007, 07:52 PM
    Very old system. If the valve requires 750 Mv you might be a little short of the required voltage to open the valve. The pilot generator (power pile) might have to be replaced. All the parts are still available. Check Ebay for replacement.
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #3

    Oct 12, 2007, 09:26 PM
    I agree with hvac1000 the Mv are a little short. You can get a thermalpile at any hvac supplier.
    guyinsb's Avatar
    guyinsb Posts: 11, Reputation: 1
    New Member
     
    #4

    Oct 14, 2011, 08:35 AM
    I read another post from someone who claimed to have a spec sheet for the B60 valve; the poster said the valve only required 250mv to operate. My B60 valve works fine, and I have consistently measured the voltage at around 400 mv. A full 750 mv might in fact be undesireable; some voltage drop is generally anticipated by the resistance along the control wire up to your thermostat or other safety control. Those valves will fail at some point, obviously. But mine is 70 years old, and still amazingly reliable. It does get "stuck" once or twice a year, usually just after a major change in the weather. I very much would like a recommendation for a replacement part, just to have a spare.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Gravity furnace & 2-wire thermostat [ 2 Answers ]

My sister has an ancient Biltwel Gravity Furnace in her basement that just stopped working. For four years she has just jumpered the thermostat wires upstairs to run the furnace. (Thermostat face completely gone.) There are only two wires coming into the thermostat and NO 110 VAC. In the...

Maytag gas dryer, replacing gas valve coils [ 5 Answers ]

Hi, I hope someone can help me. My Maytag gas dryer's igniter glows but then no flame appears. I believe it is the gas valve coils that are bad, so I purchased a replacement kit (3 coils). The instructions say to match the colors of the wires, but my replacement kit has red, black, white...

Gravity Floor furnace [ 4 Answers ]

I have a pilot light lit and the thermostat is connected, tried switching 2 wires at thermostat but this did nothing. What next please

Gas valve noise on main valve engagement [ 1 Answers ]

I have a carrier 58gs100ga furnace with a white rodgers 36e93 gas valve. The main gas valve solenoid chatters or rattles for a split second before it stays engaged after the pilot is proved. I just replace the spark/lock out board and the fan board for a different problem. This chatter is...


View more questions Search