    I'm confused about calculations re: 100 Amp sub ser
    Earlier you recommended a 2 cooper or 1 alum. Cable for a 150 ft. run to a pole barn.

    From previous posts you suggested a 4/2 cable from post lugs out to the sub panel.

    What I do not understand is the following:

    If you need to determine what size cable you first define the needed amperage +10%.

    So if the actual draw on the line is 110 Amps, how do calculate an 80% usage?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 3, 2007, 02:56 PM
    First, I know that a residential 100 amp feeder is allowed to be #4 copper (85 amps) or #2 al (90 amps).

    A circuit is assumed to run continuous, 3 hours or more, and will be derated by 80%.


    Using the 75 Deg C column of Table 310.16 of the NEC,

    110 amps time .8 = 88 amps, so a feeder branch will be assumed to carry the max of 88 amps. Next size wire is #3 copper.

    A residential 110 amp feeder is allowed to be #3.

    Doing voltage drop calcs, assuming the same 130 feet, #2 is needed to keep the Vd at or below 2%, at 1.8%.

    Recommended feeder can be 2%, plus 3% at the branch circuit level,or vice versa, depending on the length of either.


    Did I answer your question?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Running two 100 amp main panels from a 200 amp service [ 27 Answers ]

Greetings! I live in a rural country area. The electric company will be installing a pole, meter, and 200amp service with disconnect at pole. (It will require 50 foot run of service cable from pole to main load center in mobile). Currently the double wide has a General Electric 100amp Main...

Do I need 200 AMP service or is 100 AMP enough [ 1 Answers ]

I have purchased a new home (not built yet) near Toronto, Canada. The standard service is for 100 AMPs. An upgrade to 200 AMPs is available for $800. I don't want to spend the money if I don't need to. I will have electric washer/dryer, stove, fridge, dishwasher, and central air. The...

100 Amp Subpanel from 200 Amp main panel [ 2 Answers ]

I want to install a subpanel to be used to supply branch circuits to a new kitchen, laundry, garage, and some additional lighting and receptacles. The 200 amp main panel is about 50 ft away but because of the obstructions, we'll need about 85 feet of cable to connect the 100 amp subpanel. Since...

Using 100 amp panel on 200 amp service [ 5 Answers ]

I am building new camp at a site that already has 200 amp service. My power requirements are small and 100 amp will be more than sufficient. Is there any reason I cannot hookup a 100 amp panel to the 200 amp meter socket? Not sure is code allows this. I want to use a small 100 amp panel vs the...

60 amp or 100 amp service? [ 3 Answers ]

When I bought this house built in 1956 everyone who I talked to told me it was 60 amp service. Looking at the main breakers for the incoming power there are two 50amp breakers ganged together. So I have 100amp service how do I find out for sure or is my math wrong and current in parallel is still...


View more questions Search