    I'm confused about calculations re: 100 Amp sub ser
    Earlier you recommended a 2 cooper or 1 alum. Cable for a 150 ft. run to a pole barn.

    From previous posts you suggested a 4/2 cable from post lugs out to the sub panel.

    What I do not understand is the following:

    If you need to determine what size cable you first define the needed amperage +10%.

    So if the actual draw on the line is 110 Amps, how do calculate an 80% usage?
  • Oct 3, 2007, 02:56 PM
    tkrussell
    First, I know that a residential 100 amp feeder is allowed to be #4 copper (85 amps) or #2 al (90 amps).

    A circuit is assumed to run continuous, 3 hours or more, and will be derated by 80%.


    Using the 75 Deg C column of Table 310.16 of the NEC,

    110 amps time .8 = 88 amps, so a feeder branch will be assumed to carry the max of 88 amps. Next size wire is #3 copper.

    A residential 110 amp feeder is allowed to be #3.

    Doing voltage drop calcs, assuming the same 130 feet, #2 is needed to keep the Vd at or below 2%, at 1.8%.

    Recommended feeder can be 2%, plus 3% at the branch circuit level,or vice versa, depending on the length of either.