    Broken down york heatpump
    I have a York heatpump, outdoor package unit last week the weather cooled down and we switched the t-stat off, last night I noticed the emergency heat light was on, I switched the t-stat to cool and the air handler comes on but not the compressor, and the emergency heat light remained on. I cycled power on the unit and after about 1 or 2 minutes the emergency heat light came back on. What's up can anyone help me??
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #2

    Sep 22, 2007, 07:28 PM
    Check your breakers going to the a/c unit. If your heat pump faults out the aux heat takes over. If you change it back to cooling will the heatpump run?
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #3

    Sep 23, 2007, 12:26 PM
    Does your thermostat have a switch to put it in emergency heat? Some of the older stats had this switch.
    jlewis's Avatar
    jlewis Posts: 2, Reputation: 1
    New Member
     
    #4

    Sep 23, 2007, 05:54 PM
    Quote Originally Posted by acetc
    does your thermostat have a switch to put it in emergency heat? Some of the older stats had this switch.
    Yes it has but the emergency heat light stays on in off, cool, heat positoins and we are trying to cool but the compressor want come on the air handler will.
    GE1223's Avatar
    GE1223 Posts: 30, Reputation: 2
    Junior Member
     
    #5

    Feb 9, 2008, 05:45 PM
    Take the cover of the t-stat off and plce a jumper between the R terminal and the y terminal if the compressor comes on remove the jumper relace the cover and turn the t -stat to cooling with the temp lowered enough for it to come on if it does not come on the tstat is bad

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heatpump won't turn off [ 3 Answers ]

My trane heatpump won't turn off at the thermostat. The thermostat can be in the off position yet the unit will still operate. It can go from heat to cool on the cool setting. It appears as if the thermometer is working but the unit runs constantly only to turn off with the circuit breaker.:(...

Installing heatpump or AC [ 5 Answers ]

Hi I'm remodeling a house built in '32, with an addition in the 40s or 50s. The house is about 1200sq ft (800 sq ft w 9' ceilings, 400 sq ft with 8'ft ceilings) with a 1/2 basement where the heater (oil) water heater, circuit panel etc. At present there is no AC in this house, although the air...

How to replace transformer on York heatpump [ 6 Answers ]

While I was replacing old Honeywell 7day programmable thermostat with new Ritetemp touch-screen programmable thermostat, something went wrong and now I have no fan nor heat. The phone support at ritetemp suggested that I must have blown fuse of the transformer. I have 12yrs old York Heatpump...

Heatpump thermostat [ 1 Answers ]

I have a goodman heatpump with a janitrol 1890 thermostat it has never switched the aux heat on .When the temp gets too cold for heat pump to make heat .I have to turn emergency heat on myself .Book says model1860 thermostat is what should be installed is this my problem if so a new thermostat...

Runaway heatpump [ 5 Answers ]

I have a 1400sq foot 2 story home built in 2005 with a single heat pump. The thermostat is located on the first floor. During the winter the heat will run and run to try to maintain the temperature on the first floor but the second floor will bake. For example, the first floor may be set to 70 but...


View more questions Search