    50 amp Sub Panel
    Hello All, My house is very old and the main disconnect is a 100 amp fuse panel with no ground. I am adding a 50 amp subpanel in the attached garage with 6 circuits. The run to the subpanel is 70 ft of 6/3G. I have added a grounding rod for the subpanel @ the main disconnect. It appears that the neutral on the main is bonded to the enclosure. So my question is: In order to keep the neutral and the ground separate for the subpanel must I insulate the ground wire from the main panel enclosure and wire directly to the ground rod?

    Thanks
    Steve
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Sep 19, 2007, 08:20 PM
    A little difficult to follow you. Your saying all the right words but in an odd order.

    The service may be grounded to a city water system also, so don't assume the system is not grounded.

    The ground rod or rods or ground to city water is needed to be connect to the neutral bar at the main service disconnect or at the neutral of the meter.

    The neutral and equipment ground wire from the subpanel need to connect to the main neutral bar in the panel if the main is in that panel.

    At the subpanel, the neutral wire will connect to the neutral bar that is insulated, and not boneded to the metal can.

    An equipment ground bar must be added to the subpanel, bolted directly to the metal can using machine screws ,and connect all bare ground to that bar.

    Does this clear this up for you?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

200 amp panel feeding a 100 amp panel roughly 130' away [ 7 Answers ]

Hi all, We are building a apartment above the garage,my question is what size wire do I need to run from the 200 amp panel to the 100 amp panel roughly 130' away? I want to use aluminum wire as I think copper would be to costly. Thanks for your help in advance, Dude :eek:

200 AMP Service panel to 200Amp Sub Panel [ 1 Answers ]

I getting new 200Amp service to surface mount service panel. I want to run 2oo cable to bring it sub panel in my Garage which is approx 120Ft Run through ceiling. 2 Questions 1. Is there any ristriction on running a 200AMP inside house to garage ? 2. I got a dirt cheap subpanel that has...

220 amp Panel vs. 300 amp Panel [ 5 Answers ]

We are building a new 3650 square foot home in Land O Lakes Florida with the builder David Weekly. We do a LOT of exterior Christmas lights; and we requeste that eight external GFI's be placed at our roofline two on each side of the house to accommodate our wiring needs. We asked that every two...

100 Amp Subpanel from 200 Amp main panel [ 2 Answers ]

I want to install a subpanel to be used to supply branch circuits to a new kitchen, laundry, garage, and some additional lighting and receptacles. The 200 amp main panel is about 50 ft away but because of the obstructions, we'll need about 85 feet of cable to connect the 100 amp subpanel. Since...

200 Amp Service Panel with 60 Amp Main Breakers [ 26 Answers ]

I was told when we purchased our house that it had 200 Amp service which it appears to be; however, the top of each bus bars only has 60 Amp breakers for the Main shut offs. Is this normal? Each bus bar is connected to a hot wire (one red and one black) and then the two 60 amp breakers are...


View more questions Search