    Blower stops works when I give it a push
    My blower stops in my OLD carrier furnace with the air on. It will work again when I give it a push with my hand. And then lasts a few hours and then its back downstairs for another push. What can I do to fix this. I put a new main board in last year... thanks:)
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Sep 7, 2007, 01:51 AM
    Try a new motor run capacitor. If that is not it the motor might be defective/going out on overload. When you go down to push it as you say is the motor body hot?
    Jimmy prince's Avatar
    Jimmy prince Posts: 9, Reputation: 1
    New Member
     
    #3

    Sep 7, 2007, 01:52 AM
    No in fact its cold.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Sep 7, 2007, 01:55 AM
    OK then try the capacitor first. Is there 120 volts to the motor when it is supposed to be running and it is not?
    Jimmy prince's Avatar
    Jimmy prince Posts: 9, Reputation: 1
    New Member
     
    #5

    Sep 7, 2007, 01:57 AM
    Yes
    Jimmy prince's Avatar
    Jimmy prince Posts: 9, Reputation: 1
    New Member
     
    #6

    Sep 7, 2007, 02:59 AM
    Now I go down and the motor is very hot. Now what? It still works when I push it by hand still. But goes out after a hour or so.
    Jimmy prince's Avatar
    Jimmy prince Posts: 9, Reputation: 1
    New Member
     
    #7

    Sep 7, 2007, 03:51 AM
    Even though the motors hot it still works until it get to the temp. then it won't start again until I hand start it. I set it at 71 when it got to 71 it shut off and didn't come on until I did it by hand. That took 45 min. the next tim I set it for 68 this time it took a hour and a half before it reached that temp. it shut off and didn't go back on until I did it by hand again. If it was the motor wouldn't it shut off before it reached the disired temp? I think it would run all day if I set it at 60 or something.
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #8

    Sep 7, 2007, 02:18 PM
    Once again, test the run capacitor.
    Jimmy prince's Avatar
    Jimmy prince Posts: 9, Reputation: 1
    New Member
     
    #9

    Sep 7, 2007, 02:21 PM
    Yes That's For Sure Thanks. I Replaced The Condenser And Its Been Working Fine. Thanks For All The Help.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Kenmore Elite dryer - Push to start, stops when button released [ 2 Answers ]

Hi, I am having the same problem many of you out there have experienced. I purchased a new Kenmore Elite Electric Dryer 2 years ago. I have read all the responses posted here. I have taken the lower front panel off, totally cleaned the insides, and tested the contacts for continuity that were in...

Heat Pump Blower Motor Stops [ 1 Answers ]

I have an older Rheem heat pump. The blower motor on the outside unit stopped running. It seemed to only run at about half speed for a couple of minutes then get hot and stop. I replaced the motor and both capacitors. This motor runs at full speed but gets hot and stops after a couple of minutes....

Squeaks when blower motor stops [ 1 Answers ]

Were are the oil ports on the blower motor my furance ia a Hiel any one know were to oil the pots? Gibby1000

Blower works intermittently for A/C [ 1 Answers ]

I have an old York furnace with central air. When turning on the A/C, sometimes the blower comes on, sometimes it doesn't, and sometimes it toggles off and on with a loud clicking sound. If I use the manual switch on the limit control, everything is fine, but of course, then the blower is on...


View more questions Search