    Trane 803 thermostat with Dehumidity Control
    One simple question. If the dehumidity level is set for 50%, shouldn't the humidity remain at that level. It moves up and down from 50% - 55%. I understood that was the purpose of this control. To control the humidity at a constant percentage. Have I misunderstood?
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #2

    Aug 21, 2007, 04:23 PM
    Even the best systems half to have a certain amount of differentiat in the settings, if it did not then it would be constantly on and off. If it floats between 50 and 55 when set at 50 I would call this OK. Now there are more precise humidity systems in commercial applications, regards, Mike
    Maddie12's Avatar
    Maddie12 Posts: 8, Reputation: 1
    New Member
     
    #3

    Aug 22, 2007, 01:04 PM
    Quote Originally Posted by Maddie12
    One simple question. If the dehumidity level is set for 50%, shouldn't the humidity remain at that level. It moves up and down from 50% - 55%. I understood that was the purpose of this control. To control the humidity at a constant percentage. Have I misunderstood?
    Well obviously I misunderstood the installer. I thought he said that if I set the dehumidity control at 50%, the system would maintain the humidity @ 50% .

    We have a Trane XL16i with variable speed air handler.

    I've just felt uncomfortable about some of the answers I've been given by the installer.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Replacing Control Board on Trane Unit [ 17 Answers ]

Hello, Does anybody have any experience replacing the control board (CNT 03798) on a trane unit? I had an HVAC guy check out the unit, and he told me that was the part that needed replacing. I'd like to do it myself to save several $100.00 on the job, but I've never done it before. It...

Trane XL16i, Variable Speed Air Handler, 803 thermostat [ 3 Answers ]

We purchased this unit about 8 weeks ago and it's been nothing but a headache. Trane's field rep came out Friday with the installer and they gave the unit a complete going over. Checked duct work, everything. Even replaced the thermostat. Was assured everything was mechanically correct. The...

Trane XL 16i, humidity control [ 5 Answers ]

We recently purchased a Trane 16XLi with a variable speed air handler. According to their ads, the unit has the ability to remove up to 24 gals. Of moisture per day. With the temp. set at 75 degrees, the humidity is running at a minimum of 55% at night and 57%-61% during the day. I've read that...

Old Trane thermostat to new Honeywell [ 1 Answers ]

Hi We are trying to install a new honeywell themostat model rth230b. Our old one is a trane baystat240 model 3aat80b1a1 problem being seven wires with no clue what colors or letters are for what?? The new thermostat seems to have five wires can this connection work and do you know the diagram...

Old Trane thermostat to new Honeywell [ 2 Answers ]

Hi We are trying to install a new honeywell themostat model rth230b. Our old one is a trane baystat240 model 3aat80b1a1 problem being seven wires with no clue what colors or letters are for what?? The new thermostat seems to have five wires can this connection work and do you know the diagram...


View more questions Search