    Breaker problems
    I have been having problems with my 40 amp breaker tripping on my 5 ton unit. It is a basic 40 amp breaker. I have had it looked at and was told that I need to put a 50 amp breaker that is rated as a HACR breaker. He also said that a 40 amp HACR breaker would possibility do. When a test was ran it showed that the lock loader amps were pulling 33 amps to start the compressor, which is pulling almost all the amps on the basic 40 amp breaker. I was told that it was having to work to hard.

    Does this sound like a solution?
    Fr_Chuck's Avatar
    Fr_Chuck Posts: 81,301, Reputation: 7692
    Expert
     
    #2

    Aug 4, 2007, 06:55 PM
    I am putting an answer, so it will be brought back up to the top of the question lists.

    Putting in a 50 amp breaker sounds like something I would do, but properly, one needs to look at what the unit is rated and if it is drawing a lot more than listed, one needs to have the unit checked to see if there is something from with the motor or compressor causing this.

    The only thing I may question is the size of the wiring, to be sure they are listed for 50 amps. If the people telling you this are licensed to do electrical work, I would guess they checked, but I would ask to be surer.
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #3

    Aug 4, 2007, 07:20 PM
    I agree with Fr_Chuck, look on the name tag on the A/C and it will tell you what the max. size breaker or fuse can be , then make sure the wiring is capable of carrying the amps draw of the larger breaker and also make sure the fuses are the same size as the breaker.
    I believe a 50 amp breaker is fine for a 5ton unit.
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #4

    Aug 4, 2007, 08:51 PM
    You all are right,, is very,very important that the wire is heave enough to carry 50 amps of power,, is this is correct you still could have a weak breaker that can`t handle the heat
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #5

    Aug 4, 2007, 09:14 PM
    Instead of putting in larger amp fuses you need to find the cause of the fuses blowing, it could be something as simple as turning your thermostat up and down too fast, or burned points on the contactor. If you don't have the knowledge or the tools to check all of the things that have been suggested I recommend you call a service man.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Theory of vacuum Circuit Breaker & sf6 circuit breaker [ 15 Answers ]

I want to know about the basic Theory of vacuum Circuit Breaker & sf6 circuit breaker

New 15A breaker trips main 100A breaker [ 6 Answers ]

Hi, I've been finishing my basement and I added a few 15A breakers One room has 8 outlets in series with the first starting about 6 feet from the main panel. There is currently no load on this outlets. When installing the drywall I accidentally shorted the outlet closest to the panel. It...

Can I switch a 15 amp breaker to a 20 amp breaker? [ 1 Answers ]

:confused: can I switch a 15 amp breaker to a 20 amp breaker? I just bought a home tanning bed and the plug has a horizontal plug which won't fit in a regular outlet. I bought a 20 amp outlet and installed it. The tanning bed tripped the circuit breaker. I got a 20 amp circuit breaker and replaced...

Replacing a circuit breaker with a GFI breaker- q on neutrals [ 1 Answers ]

In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!

Strange Breaker problems with Heat pump and AC unit [ 1 Answers ]

Recently we have been having strange issues with our breakers. :confused: Typically if we have more than 2 appliances running in the kitchen, the GFI outlets will pop the breaker. We just reset it, and try not to use too many things at once. This is fine. :rolleyes: But... yesterday, I...


View more questions Search