    Baffling issue with baseboard heaters and AC readings
    My house has a combination of baseboard and ceiling cable heat. One baseboard has been nothing but trouble - just a small 24", 500 watt unit for the laundry room. It shares a thermostat (SPST) with a 1000 watt baseboard in the bathroom - which is the next room. That heater has worked great for the 50 years this house has been standing. But this location had the original heater fail when the house was new.

    While doing some updating last winter, I finally replaced it. That unit failed immediately. Got weak heat from a cold start for seconds, then dead. Figuring I had a bad unit, I replaced it with one that worked right away and did for a couple months. Until it too died. No heat... but the other heater on the circuit heats like mad.

    With power cut, I've found that the high temp cutoff is closed, and the element reads 17 ohms (wires disconnected). With power restored, the 2 leads each measure 125 volts in reference to ground, which is right for this house' AC coming in. But across the two - 0! They are in phase. Also the thermostat makes no difference - always 125VAC to ground x 2 and 0 VAC across the hot lines. No wonder I have no heat!

    I have not checked the other heater for voltage feed, voltage drop, resistance, etc. Also I have not removed the leads from the working heater and rechecked the dead heater, thinking I am getting a false 125 volts on one of the legs due to one leg passing current through the working element.

    Where should I go from here? I know enough circuit tracing to confuse myself!!
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #2

    Jul 25, 2007, 09:05 PM
    I know what you are saying about confusing, the reading across the thermostat would be correct. The thermostat is nothing but a switch that connects one wire to the other, the high temp. limit is closed which is correct because it is also a switch to complete the circuit to the heater. Think of electricity as water flowing through a pipe the flow (current) goes from the breaker to the thermostat through the limit to one side of the heating element and out the other side of the element and back to the breaker panel to a neutral (115 Volts) or a different leg of the incoming power (230 Volts)
    When you check for voltage across the thermostat and you get 125 volts to ground on each side but "O" volts when checking across this means that the thermostat is closed and calling for heat, you should also get the same reading on the limit switch.
    Now we get to the heater element, THIS IS NOT A SWITCH, this is the load and you should see voltage across the element (two wires connected to heater element) and the element should be getting hot, if it is not getting hot then it may be burned out and you can determind this with an OHM meter, if does not register a resistance in the wiring then it is bad.
    If for some reason you may get a voltage reading on both sides of the element to ground but "0" voltage across it then the leg (wire) leaving the heater is not completing the circuit back to the breaker panel. Hope this is helpful. Mike
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #3

    Jul 25, 2007, 09:21 PM
    If you can find these two wires in the breaker panel they should read voltage across them, perhaps a bad breaker or bad wire connection.
    TheKid72's Avatar
    TheKid72 Posts: 2, Reputation: 1
    New Member
     
    #4

    Jul 25, 2007, 09:26 PM
    Mike, Thank you for your input. You have given me a couple troubleshooting ideas, and I'll do some more testing.

    I was puzzled by the 125 volts on each leg - both in phase, but that was tested without a load from this heater. The other heater (wired in parallel) could easily cause that false reading. I will disconnect the other heater's element and retest.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

2 baseboard heaters, 2 thermostats [ 5 Answers ]

I have ran a 12/2 up to a point where I want to power two 1500 (240v) watt baseboard heaters each running off a separate thermostat. Each heater will heat a separate room. I have double-pole wall-mount thermostats. Do I split my 12/2 and go to the thermostats or is there another way this should...

New to baseboard heaters [ 24 Answers ]

Hello; I need a lot of electrical help/advice. I am trying to install an electrical baseboard heater in a basement room (15'X10'). My friend helped me already do the following: Run the conduit and electrical box for thermostat Pull all the wires Mounted the baseboard heater to the wall We...

Electric baseboard heaters -wiring 1 thermostat to two heaters [ 2 Answers ]

I would like to heat my new garage with electric baseboard heaters. The new garage is 20X24 feet. I would like to use only one 240V #12 2 wire circuit running two heaters at a total of 3800 watts. I plan to use 2 pole 20A breakers and 2c #12 wire. I would like to have both heaters controlled...

Baseboard heaters [ 1 Answers ]

Hello, Are there any rules for running #10 to Junction boxes in basement right below heaters and tapping off with 12/2 to them less than 6'. I'm running 30 amp circuit for 6000 watts of baseboard heat in parallel

Baseboard heaters [ 12 Answers ]

Hi all.. New to the forum.. Thanks in advance for any help.. I am trying to set up new baseboard heating in my basement.. My questions are to what size breakers to use and if I can put it all on one circuit.. I want to set up 3 rooms: Room 1 - 2 1000 watt heaters Room 2 & 3 - 1 1500 watt...


View more questions Search