    Condensate line not draining
    I have a problem with my condensate line on my furnace. One year ago my 3/4" condensate line cracked and had to be replaced. I replaced it with a similar 3'4"pvc pipe which id piped to hang over my floor drain in my basement. I notice gurgling noise coming from the pipe. I checked with different people who were familiar with hvac and they told me I should have a trap in the line so I installed one. Although the line is below the drip pan in the furnace it would not drain and the condensate would drip out of the back of the furnace cabinet.
    I run my furnace fan all the time and the AC is in cool so it comes on whenever the thermostat calls for it. I have a feeling there is a vapor lock problem because when I pulled the front cover off the furnace while it was running water streamed out. When I put a filter in it is soaked in just a few hours.
    I have an electric furnace with an outdoor heat pump.
    Does anyone have any suggestions?
    Thank you,
    Sam
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #2

    Jul 21, 2007, 09:43 AM
    Do you have a dip or sag in the condensate line ? This would make a double trap causing an air lock, do you have a vent on the leaving side of the trap ?
    Sam 1's Avatar
    Sam 1 Posts: 3, Reputation: 1
    New Member
     
    #3

    Jul 21, 2007, 12:12 PM
    acetc,
    Thank you for answering my question. The line has 1 90 coming out of the furnace runs about 15" to another 90 turns down to another 90 turns left to a 90 to another 90 turns right to another 90 to the drain. I have the line coming out of the furnace on a small decline. I have removed the trap and I have no vent at all.
    Sam

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bathtub draining slowly , tried to fix, not draining at all now [ 2 Answers ]

Hello, my first time here. My upstairs bathtub was draining slowly, a plumber here to snake the cesspool suggested something. First off, it is the big one piece fiberglass shower/tub fixture. I think it's a really common & standard setup, nothing fancy. I took the sifter plate off the...

Routing an AC condensate line [ 1 Answers ]

I am having an 80% downflow furnace and a 3 1/2 ton AC installed and would prefer to not have the condensate line make a swampy/muddy mess by dripping outside of the home. What options are there for routing it? Zoop

Constant draining in condensate line [ 1 Answers ]

I have a Bryant central air systems, and have noticed that there is a constant dripping stream of water coming from the condensate line. I can understand this during cooling in the summer, but should it be doing this during the winter? Also - I've tried cutting back on system use, but the...

Condensate line cleaning [ 5 Answers ]

I have to clean out a 3/4" condensate line on a 3 story building. There are 2-90 degree elbows and then a straight run of 30". Is there a snake or tubing jet that I can use to clean out. Jim

Freezing condensate line [ 1 Answers ]

A 95 % high eff furnace was installed in my attic and the condensation line , which was routed out side is freezing after it exits the home. Any options other than replacing unit w 80%


View more questions Search