    10/2 wire for a 230volt/20 amp airconditioner?
    :confused: Can I use a 10/2 house wire for a 230volt/20 amp air conditioner? And if so how do I connect the 10/2 wire to the two breakers in my electrical box?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 23, 2007, 02:23 PM
    Yes the #10 can be used for a 20 amp circuit. The #10 will connect to the terminals of the breaker. Not sure how else to answer that question. Is there something specific I can help with?
    jeffgrab24's Avatar
    jeffgrab24 Posts: 2, Reputation: 1
    New Member
     
    #3

    Apr 10, 2010, 03:35 PM

    Yes you can use a 10-2 wire to wire your air conditioner.you need a 2 pole 20amp circuit breaker wich is actually 2 separate cir.breakers connected with a bar.now you put the black wire under one lug of the 2 pole breaker and the white wire under the other lug.the bare wire obviouly is the ground which go's on the nuetral bar.There is no nuetral on a 220v.air conditioner.now you need a 220v plug to plug you ac into. Black wire to one side and white to the other and bare to ground screw.theplug will have brass colored screws on both sides where you land your hot wires
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Apr 10, 2010, 06:29 PM

    Whoa Jeff.

    If the wiring is being run from the main service panel, yes the bare wire can be connected to a Neutral Bus Bar because both Neutral and Ground are bonded together in the Main Service Panel. If the Circuit is being fed from a sub, then No. The bare wire must be connected to the Ground bus.

    Also, 10/2 cable will require you to permanently mark the white or gray conductor to a color other than gray, white or green. Use sharpie pens or tape to signify that the conductor is not being used as a Neutral conductor.

    This must be done at both ends of the conductor and at any openings along the way where the conductor is visible. Normally, I use Black, Red or Blue tape. In this instance, I would most likely choose to use Red.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Apr 10, 2010, 07:02 PM

    Also Jeff, it is considered very poor forum etiquite to post a reply to a 3 year old thread as if the guy is still around to read it.
    I think it is safe to say this job is all done.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Airconditioner units [ 5 Answers ]

Hi, My airconditioner unit is not coming on the outside fan is not turning and the unit is not on in the attic. I was having a problem with the hot air inside the house not going anywhere called ac guy he came out and cleaned the coil in the unit outside it worked great for 2days now nothing is...

20 amp breaker, wire gauging [ 4 Answers ]

What gauge of wire do I need to run off a 20 amp breaker?

Water Leakage from Airconditioner [ 1 Answers ]

Dear Sir, I have multiple 8 ton A/c's in the office. From few of them, water pours down suddenly. Kindly let me know the reasons the leakage happens. We have tried the following. 1) Increased the size of the drain pipe 2) we get the filter cleaned periodically 3) we have checked the slope...

Airconditioner [ 1 Answers ]

Wall unit plugged into split plug on dbl 15 breaker. After running 1-2 hrs. breaker trips. Wire warm to hot and plug receptacle warm. Is problem probably the air conditioner or perhaps plugin or breaker. Jim

60 amp 230volt home circuit needed [ 3 Answers ]

I'm going to be running a Plasma Cutter and 230V Tig welder. The plasma cutter requires between 55-60 amps maximum. I was wondering what I need to do in order to run a 230 volt, 60 amp circuit from garage mounted circuit panel, to an external receptacle outside of my basement on a concrete...


View more questions Search