    Hello: I have a two story addition on my house built by the previous owner. There is one thermostat upstairs and one thermostat downstairs. The system directs air to the downstairs through a damper. The upstairs thermostat controls the temperature and the downstairs one appears only to turn on a fan.

    The system stopped working and in my infinite wisdom I started trouble shooting, disconnecting some wires. I'm almost done but have the following situation.

    The downstairs thermostat has a Red (24v) White (Common) and Blue (Fan) wires connected to it. I disconnected the blue wire both at the thermostat and at the 24 volt transformer and now don't know how to reconnect it.

    My question is: Where should the Blue wire be connected at the 24 volt transformer? At the hot (24 volt side) or at the Common side?thanks in advance.

    Richard
    tazdec's Avatar
    tazdec Posts: 2, Reputation: 1
    New Member
     
    #2

    Jun 21, 2007, 02:50 PM
    The blue wire will not go to your transformer at all it will go to a relay or fan center if you take that blue wire and touch it to the red one a relay will close and the fan should come on. On most residential houses there is no common to the thermostat r is hot g is fan y is cooling , if you have a damper r would nomallly be power [hot] the other two would either power the damper closed are open
    dahrich's Avatar
    dahrich Posts: 4, Reputation: 1
    New Member
     
    #3

    Jun 21, 2007, 05:07 PM
    Hi:
    Thanks for your reply>
    I'm afraid I don't understand your answer.
    There is a "C" terminal on Thermostats which is the comon side of the 24 volt transformer.

    The Blue wire is so located that there is no place for it to be connected except to one or the other sides of the 24 volt transformer.

    Richard
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #4

    Jun 21, 2007, 05:56 PM
    It is hard to say because you are in a realm of unstandardized wiring, the installer knew what he was doing and only with a blue print would I advise you on what to do.
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #5

    Jun 21, 2007, 05:58 PM
    Actually I would go as far as to say if this is a zone system, there should be a zone control board to control the dampers and HVAC system. I hate those hacks that try to skirt the additional cost of doing it right when they damper different zones.
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #6

    Jun 21, 2007, 06:44 PM
    You do have a zone system from your description. Some of the older zone boards told the blower when to come on(it controls the blower). The master T-stat was the only stat that had the G circuit hooked up to control the blower. You may be in luck if you have a three zone system and only using two zones. If zone two was bad, move the T-stat wires and zone damper wires to zone three. It's a good chance it will work.
    dahrich's Avatar
    dahrich Posts: 4, Reputation: 1
    New Member
     
    #7

    Jun 22, 2007, 12:29 AM
    Thanks fellows for you insights.

    T-Top your comment is a good one but unfortunately it is a two zone system.

    Checking the control board the master T-stat has one G wire and from what I know does control the blower and damper.

    At the control board terminal strip there are two cables connected. One cable has 5 wires going from the terminal strip to the master T-stat. The other cable has only two wires, Red and White - the Red wire is inserted into the Y slot and the White wire into the C slot.

    I thought this cable went to the downstairs T-stat but now I'm not sure because at the downstairs T-stat the Red wire is in the R slot and a White wire in the C slot. And I think the Blue wire is to be inserted into the G slot.
    Does it make sense that the Red wire at Y on the control board terminal strip would go to the R slot on the downstairs T-stat terminal strip?
    Also, at the 24 volt xformer there is the cable with Red, White and Blue wires that I thought went to the downstairs T-stat. The Red wire is connected to the 24 volt side of the xformer and the White wire to the common side of the xformer. Thses wires are the ones which raided the question about where should the Blue wire be connected.

    However, since the cable at the control board terminal strip has a Red wire conneced to the Y slot I am in total confusion. Is it possible these are not the same cable? I will try to determine if they are the same cable.

    Please let me also ask a few more questions:

    1. At the downstairs T-stat there is a jumper between Y and W. Anyone have any idea what this is for?

    2. If the downstairs T-stat doesn't turn the fan on and off what is its purpose?
    Is it only a thermometer?

    3. If the upstairs T-stat is Master and controls the fan and damper how does it know how much to open the damper to cool the downstairs if the downstairs T-stat is only a thermometer.

    3. When I check the upstairs T-stat I get 24 volts from Red to Green and 0 volts common to Green. Does this imply that the Blue wire to the downstairs T-stat should be connected to 24 volts at the xformer and to the Fan connection at the downstairs T-stat?

    I need to do more checking and if you bear with me I'll be back with more information.

    Thanks for all your help.

    Richard
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Jun 22, 2007, 01:48 AM
    If you smell smoke you know you wired it wrong. You have a much more complex system than the standard residential heat system. Without being there it is near impossible to know the layout of the original system. Most were laid out on a if come on basis. That is if the thermostat called it would come on and by pass the setting of the other thermostat. The bypass would also activate a relay and run the blower motor weather or not the main stat is calling for heat or cool.

    I would draw a complete map of the entire system before you start to pull wires off here and there other wise you could get into some trouble.
    coronado2412's Avatar
    coronado2412 Posts: 9, Reputation: 1
    New Member
     
    #9

    Jun 22, 2007, 04:00 AM
    Richard, You are a brave soul to try to diagnose the problem, however, your system is a "field constructed" control circuit. Typically, systems have their own transformers and thermostats. You seem to have a modulating control that positions dampers by changes to a temperature sensor. May I politely suggest that you call a licensed air conditioning contractor and explain the circumstances. They all seem to have at least one technician able to solve your problems. PS... blue wires are generally used to tie in all of the controls to the secondary side of the transformer. Red is the input side that leads to the various control relays or contactors through switching devices, i.e. auto/on, cooling, heating, emergency heat, and LED indicators. If you have lights on the thermostat, the blue is usually the secondary side (L2) that power the lights... If there are no lights or indicators, then everything will work from the red through green (fan) yellow (first stage heat or cooling) orange (reversing valve if a hat pump).
    dahrich's Avatar
    dahrich Posts: 4, Reputation: 1
    New Member
     
    #10

    Jun 22, 2007, 04:17 PM
    Hello:
    Well, I was able to talk to the contractor that installed the air conditioner and he cleared up all my questions.

    FYI: The upstairs T-stat is the master controller. The downstairs T-stat controls only the opening and closing of the Damper depending upon the temperature in the room and the T-stat setting.

    The jumper on the downstairs T-stat is also connected to the white wire that goes to the Damper and allows this T-stat to open/close the Damper regardless whether it is calling for heating or cooling. I had wondered if this T-stat could be replaced with an On/Off switch and the contactor said it could. A switch would greatly simply the understanding of what this T-stat does.

    The second cable at the control board terminal strip (Y and C connection) controls the compressor.

    I can now relax a little as this has been a very, very frustrating experience particularly because I did not understand the operation of the downstairs T-stat.

    Thank you for all your help.

    Regards,
    Richard

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Carrier air handler 24 volt transformer. [ 15 Answers ]

Last week my air handler quit working, I found that the 5AMP fuse for the secondary 24volt pwr supply was blown, replace and all worked fine for a week. Now I find it blown again, but each time I relace it it blows, The voltage reading I get at the fuse is 29.5 V is that to high? The transformer...

Air conditioning [ 1 Answers ]

L moved to my new home last winter,and this summer tried to run the A/C the outside unit is not running at all .Look like when l was moving in someone pulled out some wires which run from the outside unit l think to the 24v trans or the thamostart . There is two small wires how do l hook them up?

24 Volt connection on central vac [ 1 Answers ]

I just got a brand-new Hoover central vac as a wedding present and I'm trying to connect it. The instructions are VERY vague they simply say to connect the 24 volt power in the proper space. Easier said than done... I have the rough in from my contractor and the wire looks like a phone line. It has...

Air Conditioning [ 7 Answers ]

You should have 5 wires running to the outside unit. 2 big heavy, insulated ones plus a ground from the breaker outside by the unit, and a couple of little insulated ones coming out from the furnace. With the thermostat calling for cooling, the big ones should have 240 V between them and the...

Wiring 12 volt transformer [ 1 Answers ]

I have recently installed some 12 volt miniature lights in home. I have them working now but began wondering about how I have the 12 volt transformer wired. The lights are on a switch and I have the transformer in the line before the switch. Thus I have power at the transformer all the time. Is...


View more questions Search