        Carrier air handler 24 volt transformer.
       
      
    
    
    
                  
        Last week my air handler quit working, I found that the 5AMP fuse for the secondary 24volt pwr supply was blown, replace and all worked fine for a week.  Now I find it blown again, but each time I relace it it blows,  The voltage reading I get at the fuse is 29.5 V is that to high?  The transformer is 60hz/208v/230v 24 V load  40VA.  Or may it be the 24V circuit board? 
Bob
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               Uber Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Feb 2, 2007, 07:55 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        I would start by carefully going over all the control wiring.  It could be a wire has rubbed through.  I lost a couple of transformers before installing an inline fuse on my old furnace.  When I replaced it, I discovered chipmunks had chewed the thermostat wring.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Feb 2, 2007, 08:11 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        The wiring looks good.  But was wondering if the 29.5 volts out of the transformer is to high indicating a faulty transformer
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Feb 2, 2007, 08:12 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        
	
		
			
			
				
					  Originally Posted by  labman
					
				 
				I would start by carefully going over all the control wiring.  It could be a wire has rubbed through.  I lost a couple of transformers before installing an inline fuse on my old furnace.  When I replaced it, I discovered chipmunks had chewed the thermostat wring. 
			
		 
	 
 All wiring looks good.  Is the 29.5 volts out of the 24V transformer to high?
      
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               Ultra Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Feb 2, 2007, 10:55 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        No 29 volts is not to high, something else is shorting out.  Just a hunch, but look by the A/C unit for bad insulation in that low voltage wire.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Feb 2, 2007, 04:05 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        
	
		
			
			
				
					  Originally Posted by  frostrc911
					
				 
				Last week my air handler quit working, I found that the 5AMP fuse for the secondary 24volt pwr supply was blown, replace and all worked fine for a week.  Now I find it blown again, but each time I relace it it blows,  The voltage reading I get at the fuse is 29.5 V is that to high?  The transformer is 60hz/208v/230v 24 V load  40VA.  or may it be the 24V circuit board? 
Bob 
			
		 
	 
 I don't think it's a short, because the blower tries to start up.  I had it in heat put a new fuse in and reset the 220 bkrs.  I first saw a smal spark on the sequencer termianl the fuse went. Reading 29.5 volts instead of 24 also.
      
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               Ultra Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Feb 2, 2007, 04:19 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        That fuse controls the low voltage circuit of the control wiring, so it won't effect the blower.  You should not have seen a spark at the sequencer, start there.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Feb 2, 2007, 04:30 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        The 29VAC has me thinking the board may be bad or the programmable termostat.  Did disconnect all thermostat wire to the low VAC , air handler side and those going to heat pump and read between all for shorts no short. The Time delay circuit is a questionable item also or is it?
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               Ultra Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Feb 2, 2007, 04:41 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        29 volts is not an issue, I see 22 to 31 volts all the time and nothing is wrong.  The sequencer has a heating element in it that slowly closes the high voltage contacts.  The heater could be shorted out.  I really don't think it is the thermostat.  You can try disconnecting all the heat pump wires and burn up another fuse if you like.  Or observe when the fuse blows.  Ex. When t-stat is completely off? When you turn on the heat pump? Or when you turn on the emergency heat?
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Feb 2, 2007, 04:59 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Okay, just replaced fuse, turned thermostat to off but fan to on.  All works fine, blower was advertised.  Turn to heat or AC and fuse pops.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               Ultra Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Feb 2, 2007, 05:12 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Disconnect the sequencer in question and try again.  Please be careful.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Feb 2, 2007, 05:45 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        This is weired.  Turned T-stat off.  Fan on.   Fan came on.  Went to AC.. droped temp and HP came on blowing cold air.  Went to heat and it produced heat.  Went to recover and emergency, and both ran.. did put back in normal auto.  Still running.  Could the T-stat benn confused?  Did bump it hard last week when it first went out.  Maybe in H mode with  recovery or emergency to start overloads something.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Feb 2, 2007, 05:48 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        I thank you for your help.  I have been in the Navy for 29.8 yrs now as an AME (aircraft climate control, and E-ject seats).  I've learned to be safe.  Thanks again.  Master Chief Bob/KC5GOY
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jun 22, 2007, 04:21 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Secondary voltage is a product of the turn ratio between the primary and secondary side of the transformer.  i.e.  240volt input with a ten to one ratio gives 24 volts on the secondary.  Primary sides have "taps" they come with the primary side connected for a 240 volt input.  If the voltage input from the power company is less than 240volts, the secondary side of the same 10 to 1 ratio would cause the secondary side to increase voltage. The amp carrying capacity of a transformer is the secondary is the VA rating divided by the secondary voltage... in your case... 24 into 40va = 1.667 max amps.  If you have a 5 amp fuse, it should hold and not blow the fuse... look for the intermitent short where wires are kinked, pass through or by a sharp object, where water or moisture could cause a short... does the fuse go bad in the early AM when there is high humidity and dew on the ground?. 
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                | 
            
      
              
               Ultra Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jun 22, 2007, 07:12 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Carrier is known to have low voltage shorts on A/C  and heatpumps. The low voltage wires from the reversing valve coil, high pressure switch, defrost sensor and low pressure switch will rub into the discharge line of the compressor and make the fuse blow. Turn power off to both units and check the wires around the compressor to see if they are rubbing on the refrigerant lines.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Nov 13, 2008, 04:33 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        
	
		
			
			
				
					  Originally Posted by  T-Top
					 
				 
				Carrier is known to have low voltage shorts on A/C  and heatpumps. the low voltage wires from the reversing valve coil, high pressure switch, defrost sensor and low pressure switch will rub into the discharge line of the compressor and make the fuse blow. Turn power off to both units and check the wires around the compressor to see if they are rubbing on the refrigerant lines. 
			
		 
	 
 
Check the white wire coming from the defrost control board. Seems like when the system goes on defrost mode or the temp outside falls below 40F the defrost control board sends 24vac signal to the white wire to energize your aux electric heat in the indoor unit, which causes the fuse to blow, if this white wire is shorted to ground this will definitely open the 5 amp fuse.
      
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
 
 
 
     
  
   
  
   
  
  
  
  
  
  
  
  
  
  
  
  
  
  
    | Question Tools | 
    Search this Question | 
   
  
    | 
    
    
    
     | 
    
    
    
    
    
     | 
    
   
   
   
    Add your answer here.
    
    
 
Check out some similar questions!
New air handler hook up
 [ 2 Answers ]
I have a burnam oil fired boiler w/ 2 air handlers for both heating and cooling. I am adding a 3rd air handler it's the same as my others but newer and has a circuit board instead of selinoids and relays The air handler is a First Co model #36HBXB-HW, a TACO571-2 zone valve and a Robertshaw 9400...
 
 
Air handler doesn't start
 [ 2 Answers ]
My air conditioning unit outside will be running, but the air handler in the garage will not start. I have to turn off the thermostat and turn it back on to get the handler to start. Is there a switch or valve on the handler that can be replaced? It is a Janitrol
 
 
Air handler leaking
 [ 1 Answers ]
My air conditioning air handler is located upstairs in my two story townhome.  I noticed the air handler is leaking water... it leaks from under the area where you change the filer.  I noticed there is no water leaking from the pipe outside.  I put a bucket under the unit for now... is this serious?
 
 
Buzzing from air handler
 [ 2 Answers ]
Hi, 
Hoping for info concerning a buzzing sound coming from air handler.  
We live in a high-rise building(24 floors). We are on a building wide system with air handlers in each room. 
Small bedroom unit has history about this time each year(last 5) that start buzzing. Past years maintenance would...
 
 
Wiring 12 volt transformer
 [ 1 Answers ]
I have recently installed some 12 volt miniature lights in home.  I have them working now but began wondering about how I have the 12 volt transformer wired.  The lights are on a switch and I have the transformer in the line before the switch.  Thus I have power at the transformer all the time.  Is...
 
 
 