    Base board heating requirement for basement
    What would be the power requirement for a baseboard heater in a basement room of area about 250 sq ft. One side of the room (length = 16') has a standard walk out sliding glass door. I would prefer to stick with 120v device.

    Here in Minnesota, outside temperature can go below zero F, during peak winter!

    Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 19, 2007, 02:48 PM
    One rule of thumb is 11 watts per square foot, which I think would apply to your situation ,round numbers between 2500 to 3000 watts. At 120 volts a 2500 watt heater will draw 20.8 amps, and a 3000 watt will draw 25 amps. Both will need a 30 amp circuit, with #10 wire and a single pole 330 amp breaker. You should be able to find a recess heater that will have a builtin thermostat and a blower fan.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #3

    Jun 19, 2007, 03:16 PM
    I agree. I normally go 10w per sq, but it pretty much works out to be the same.
    Each environment has it's unique requirements;)
    hbuilder's Avatar
    hbuilder Posts: 15, Reputation: 1
    New Member
     
    #4

    Jun 20, 2007, 05:52 AM
    Thanks guys!
    I was hoping to get away with 12AWG. Good that I did not open the box!
    hbuilder's Avatar
    hbuilder Posts: 15, Reputation: 1
    New Member
     
    #5

    Jul 25, 2007, 05:36 AM
    All right, this is what I finally did.

    Since most of the baseboard heaters work at 240v (in Home Depot & Menards), I wired two 240v receptacles with 12/2 AWG in the same circuit - one in family room and the other in bedroom.

    Since it is a shared circuit between family room and bedroom all I have to make sure is that the total current does not exceed 20A, which is easier than leaving head-room in two different circuits.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Cement board meets shower base [ 2 Answers ]

Im finishing my basement and learning as I go. I need help with the neo angle shower base that I have already installed. I have read a couple threads that still doesn't really answer my question. Does the cement board go over the shower lip (the place that is used to screw the shower base to...

Base Board Heater [ 1 Answers ]

How Do I Wire A Double Pole Thermestate To A Baseboard Heater Using 12/2 Wiring.

Relocating Base Board Heathers and light switches [ 4 Answers ]

I have taken down a wall that separates the kitchen and living room area, and have to relocate the light switches, thermostats, and base board heaters... After letting all the wiring go from same and relocating the boxes, I've found that the original wiring is not long enough to reach the boxes...

Sizing of base board heat? [ 1 Answers ]

I am looking to put Electric Baseboard heat in a basement, it is approx. 25'w x 30'l. I am looking to put in 3 to 4 six-foot units that are 240v, 1500w & 6.3A. Will this be enough, or too much? What is the calculation for btu's to sq feet? The unit, which I selected, is 5100btu's ea. Is there a way...


View more questions Search