    Relocating Base Board Heathers and light switches
    I have taken down a wall that separates the kitchen and living room area, and have to relocate the light switches, thermostats, and base board heaters... After letting all the wiring go from same and relocating the boxes, I've found that the original wiring is not long enough to reach the boxes new location, running from the attic... Do I splice each 12/2 wire, for added length, at the site of the wire. Or do I use separate junction boxes in the attic, then use the appropriate length wiring to reach the new switches?

    Thanks in advance for any help offered.
    bhayne's Avatar
    bhayne Posts: 339, Reputation: 4
    Full Member
     
    #2

    Oct 12, 2006, 06:37 AM
    Splices are quite easy. Install a Junction Box at the splice location (in the attic). Splice and join wires with Barrets. Install a cover plate over JB.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Oct 12, 2006, 06:42 AM
    Pull up all the cables into the attic, and splice each of the cables that are too short in a junction box, onto a new cable extension that can be re-routed to the device that is needed.

    As long as the attic is accessible, junction boxes located in the attic are fine. Be sure to splice each wire properly, and use a blank cover on each box.

    Multple cables can use one junction box, but each box has a limit to the amount of wires. Need to allow 2 cubic inch for each #14 wire, and 2.25 CI for each #12.

    So, for example, say you had a typical 4x4 JB 1.5 in deep, this has 24 cubic inch of volume, and can only fit a total of 10 #12 wires. This equals 4- 2 wire cables, each black and white is counted, and all the ground wires are counted as one.
    Corey H's Avatar
    Corey H Posts: 2, Reputation: 1
    New Member
     
    #4

    Oct 12, 2006, 03:29 PM
    Thanks guys for the help... Everything is done as you have stated, aside from one wire that's running a light switch, which is spliced only using caps(no JB), inside the existing wall.. Do you suggest I use a Junction Box for this as well, or should It be fine as is?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Oct 12, 2006, 03:42 PM
    No, the splices need to be in a box, with a cover and accessible. If the box will be in a finished wall there is a good selection of blank finish plates.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

3 amp 25 volt light switches [ 5 Answers ]

I Am Upgrading A House That Was Built In 1963 And The Light Switches Have Never Been Changed,the House Was A Ge Home And All The Light Switches Are Low Voltage.does Anyone Know Where I Can Find Replacement Swithches?they Are 3 Amp 25 Volt Switches.

Problem with Hallway Light Switches [ 3 Answers ]

I want to replace my hall lights, from up and down toggles switches to the flat plate toggle. I have a switch at each end of the hallway. I purchased a Leviton switch that has 2 connectors and a green ground. The switches in my existing boxes have black, white, red and a ground. What do I need to...

Light switches [ 1 Answers ]

Here is a strange one. I am visiting my father, and he recently replaced an outlet in one bedroom and now the light switch no longer works. He didn't touch the switch at all. Here is the really odd part... now the same problem is in the adjoining bedroom. However, they are on different...

Wiring for multiple light switches [ 3 Answers ]

I have three light switches that control one light fixture. In the past, they all turned the light of and on independently. But recently it depends on where you turn if off. In some cases, it won't turn on at another switch. Someone told me it was the wiring or the switches. Nobody has changed...

Sizing of base board heat? [ 1 Answers ]

I am looking to put Electric Baseboard heat in a basement, it is approx. 25'w x 30'l. I am looking to put in 3 to 4 six-foot units that are 240v, 1500w & 6.3A. Will this be enough, or too much? What is the calculation for btu's to sq feet? The unit, which I selected, is 5100btu's ea. Is there a way...


View more questions Search