    Fluorescent ballast total amps
    Question: Are the amps listed on a fluorescent light ballast the amount continuously drawn, or the max under certain conditions?

    I recently installed some older T-12/magnetic ballast lights in my basement (got them at a good price). I added up all the amps and it comes to slightly over 18 amps. I wanted to test the illumination so I temporarily connected them to a 15 amp circuit, and it didn't trip the breaker. I've tested for several days, hours at time, with no problem. I still plan to upgrade the circuit or possibly split the lights on two circuits. Just wonder if I'm missing something here as this will help in my wiring plans. Thanks
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Aug 30, 2015, 03:59 PM
    Ballast amperage would be the maximum for that ballast.

    Amperage used would be determined by the number and size of the bulbs.

    For instance two 40 watt bulbs would draw a total of 80 watts.
    80 watts divided by 120 volts would be .666 amps.

    So, count the number of bulbs, multiply by the watts and divide by 120 for total amps on the circuit. Doubt that you could exceed 15 amps in a basement.
    afscme's Avatar
    afscme Posts: 23, Reputation: 4
    New Member
     
    #3

    Aug 30, 2015, 08:15 PM
    HK, thanks. Using that calc I have slightly over 13 amps-I installed a lot of lights w/40 watters. Will up grade to 20amp/12 gage.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #4

    Aug 30, 2015, 10:26 PM
    Will up grade to 20amp/12 gage.
    OK, but should not be necessary.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #5

    Aug 31, 2015, 08:54 AM
    Quote Originally Posted by afscme View Post
    HK, thanks. Using that calc I have slightly over 13 amps-I installed a lot of lights w/40 watters. Will up grade to 20amp/12 gage.
    Pick up a clamp on ammeter. The calcs are just to get you close, never exact.
    Too many factors to consider, from input voltage, length of circuit voltage drop, type and wattage of bulb. It's unlikely you will have to change the circuit.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #6

    Sep 10, 2015, 04:13 AM
    The rated current for a fluorescent fixture is written on each ballast...
    the lamp wattage may not always give you the correct current draw as there may be a power factor to the ballast.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Mixing fluorescent ballast [ 1 Answers ]

I have an older 4 tube fluorescent light (T12 blubs) with 2 magnetic ballasts. One ballast went bad and began leaking. I looked at the wiring on the socket ends and it appears that there is some interconnection but maybe that's just a tap wire for the parallel connection. My question is can I...

Wiring fluorescent ballast [ 4 Answers ]

Need to change ballast in fluorescent fixture. Old ballast was 4 wire, red, blue black and white - New ballast has 2 reds, 2 blues, 2 yellows, a black and a white. Now what?

Fluorescent not working - ballast and tubes are OK [ 2 Answers ]

I have two fluorescent fixtures that are exactly the same in my kitchen. They both went out the same day - I don't know if it was exactly the same moment or not. On one of them, I noticed a tube was black on one side. I replaced the tube and that fixture works fine now. New tubes did not fix...

Fluorescent lamp vs ballast [ 2 Answers ]

I have a fluorescent ceiling fixture with two circular lamps and two separate ballasts. One of the lamps is not longer lighting. Is there any way to determine which element (lamp or ballast) is defective? I have used a continuity tester to check out incandescent lamps but am not sure how to do...


View more questions Search