Apr 3, 2015, 10:33 PM
|
|
Carrier WeatherMaker 8000 Does Not Work
Woke up to temperature below where it was set, furnace not turning on.
Reset circuit and it turned on, blew cold air for about 90 seconds and turned off.
Replaced thermostat, reset circuit, same thing happened.
Opened furnace, removed flame sensor, sanded it lightly, replaced it, turned back on furnace, same thing happened.
Here's what happens when thermostat is set at higher temperature than house and I turn on and off switch at furnace
- blower goes for about 90 seconds, get error code 12
- ignitor glows red but burners do not ignite
- ignitor turns off and tries again another two times, get error code 34
Also tried pressing the reset button between two wires but that did not help
And, tried tapping gas valve when coil was red but that did not help
|
|
|
Uber Member
|
|
Apr 4, 2015, 07:49 AM
|
|
Inside your air handler fan housing should be a chart with the flash codes. Typically they will be pressure switch not closing, flame sensor or high temp limit, sometimes rollout. Yours sounds like either of the first 2. 34 is probably a lockout code. If you Google" Carrier 8000 codes" you will also find them.
|
|
|
New Member
|
|
Apr 4, 2015, 08:51 AM
|
|
thank you, code 34 is Ignition Proving Failure
It says that the control will try 3x (which it does) before Ignition Lockout which I guess means is a safety and it turns off until I reset it
It says
- flame sensor must not be grounded
- oxide buildup
- proper flame sense microamps
- gas valve defective or turned off (valve is on and gas works on my stove and hot water heater)
- defective hot surface ignitor
- low inlet gas pressure
- inadequate flame carryover or rough ignition
- green/yellow wire must be connected to furnace sheet metal
thank you, code 34 is Ignition Proving Failure
It says that the control will try 3x (which it does) before Ignition Lockout which I guess means is a safety and it turns off until I reset it
It says
- flame sensor must not be grounded
- oxide buildup
- proper flame sense microamps
- gas valve defective or turned off (valve is on and gas works on my stove and hot water heater)
- defective hot surface ignitor
- low inlet gas pressure
- inadequate flame carryover or rough ignition
- green/yellow wire must be connected to furnace sheet metal
What's my best next step? Replace hot surface ignitor?
|
|
|
New Member
|
|
Apr 4, 2015, 09:53 AM
|
|
Thank you, I've watched the videos and find them helpful but still have not solved problem
My ignitor glows orange, I hear a click but the burners do not light
My burners appear to be in good shape and I do not smell any gas
My gas and gas valve are on so not sure why gas does not appear to be flowing to the furnace
|
|
|
Uber Member
|
|
Apr 4, 2015, 11:40 AM
|
|
What is error code 12? "gas valve are on so..." How do you know the gas valve is working?
|
|
|
New Member
|
|
Apr 4, 2015, 12:57 PM
|
|
Error code 12 had to do with blower
I didn't know if gas valve was working and read that if I tap it with a screwdriver while the ignitor is orange that burners might light, but it didn't
I read someplace else that I should tap the pressure control switch with a screwdriver instead. I just did that, and it worked! I heated the house and then it turned off. I then turned up the thermostat and this time the burners came on without me tapping.
Hopefully, problem solved but will monitor
Thanks for the help
|
|
|
New Member
|
|
Apr 5, 2015, 08:25 AM
|
|
<br>
It worked for about 12 hours and then didn't light again.<br>
I reset it and tapped the pressure control switch when the ignitor was orange and it lit again but obviously something is bad<br>
Does the pressure control switch go bad or is it a sign of a bad board or something else? The board was replaced once about ten years ago
|
|
|
New Member
|
|
Apr 5, 2015, 08:56 AM
|
|
Attachment 47279
By the way, the part I refer to as the pressure control switch is the rectangular black box next to the gas valve. Is that the right name for it?
|
|
|
Full Member
|
|
Apr 5, 2015, 09:32 AM
|
|
Originally Posted by ericmj2
Attachment 47279
By the way, the part I refer to as the pressure control switch is the rectangular black box next to the gas valve. Is that the right name for it?
The attachment is not working.
|
|
|
Uber Member
|
|
Apr 5, 2015, 11:22 AM
|
|
I didn't open the link but it will have a flex tube into the inducer fan case and 2 or more wires. Remove the flex tube and carefully try to clean the orifices with a wire. Start at the inducer as that is typically where dirt will build up. They are inexpensive to replace, $20 or so.
|
|
|
New Member
|
|
Apr 5, 2015, 01:14 PM
|
|
Thanks for the suggestion but I must have described the part poorly as there is no flex tube attached to this rectangular black box.
It is located close to the gas valve and has a three wires that attach to it at two different places (two wires at one contact, one wire at the other).
Those wires are the only items connected to this part
|
|
|
Expert
|
|
Apr 5, 2015, 01:46 PM
|
|
The link you provided gives your personal info, and some nice pictures of scenery, but NO part.
|
|
|
New Member
|
|
Apr 5, 2015, 03:09 PM
|
|
Originally Posted by talaniman
The link you provided gives your personal info, and some nice pictures of scenery, but NO part.
Ugh - tried again -
View image: carrier furnace
|
|
|
Uber Member
|
|
Apr 5, 2015, 06:04 PM
|
|
Obviously that is the inducer fan in front, the black flat unit below is your high limit safety. Don't know what the arrow is pointing to, could be a pressure switch but I have never seen one directly on the gas valve. I believe the pressure switch is the device next to the inducer fan, has a yellow tag on it. Is this a 2 stage heater?
|
|
|
New Member
|
|
Apr 5, 2015, 06:41 PM
|
|
Here's a picture of the part and the area it is in from above - you can see the gas valve on the bottom right and then just above it and to the left is the black piece that I'm referring to with the wires unplugged.
http://postimg.org/image/f88tj8og9/
I don't know if it is a two stage heater
|
|
|
Uber Member
|
|
Apr 7, 2015, 05:43 PM
|
|
That is a solenoid, probably for the gas valve. The contacts are corroded or possible dirt in the solenoid slug that keeps it from retracting. Google the gas valve model, it should tell you for sure.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
FA Carrier 8000 weathermaker
[ 7 Answers ]
Getting a 12 error code. The blower starts but no ignition. I checked the ignitor seems OK and the flame sensor I lightly sanded. Still same result. Any ideas?
Carrier weathermaker 8000
[ 0 Answers ]
I have a Carrier Weathermaker 8000 furnace. When the heat is turned on, the electronic ignitor glows and fan is running. The burner does not ignite. I have turned the power and gas off to the unit and reset the unit. After turning the power and gas back on, I set the thermostat to a desired temp...
Carrier Weathermaker 8000
[ 4 Answers ]
I've had my carrier a/c heat unit for about 10 years.. . Good service, but it has recently been making a sqeaking/chirping/screeching sound when the fan is running in a/c mode. I reminds me of the sound a car makes when the fan belt is slipping. Any suggestions?
Thanks,
lankford3
Carrier weathermaker 8000
[ 3 Answers ]
I have a carrier weathermaker 8000 gas furance... when the thermastat calles for heat the furance turns on it willgo for 3 for 4 min... then the flame stops and the blower runs for the 128 seconds... this is all normal... but the thermastat is still calling for heat and the furance kick on again...