    Zone valve problem ?
    Base board heat / hot water boiler. Upstairs zone is still heating even though thermostat is set below actual temp
    Zone valve gears work when I call for heat - is the valve itself not closing even thougth the valve motor appears to work ?
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #2

    Dec 13, 2014, 06:45 PM
    Sounds like you have Honeywell zone valves. It is uncommon to have them stick open but it's not unheard of. I have seen the rubber ball inside the valve body deterioate to the point where they would not shut off the flow. Replacing the ball is a pain but often easier than replacing the entire valve. Here is a source for the rebuild kit: 272742A - Honeywell 272742A - Ball & O-Ring for Zone Valve
    Russ1111's Avatar
    Russ1111 Posts: 3, Reputation: 1
    New Member
     
    #3

    Dec 14, 2014, 09:35 AM
    Quote Originally Posted by Grady White View Post
    Sounds like you have Honeywell zone valves. It is uncommon to have them stick open but it's not unheard of. I have seen the rubber ball inside the valve body deterioate to the point where they would not shut off the flow. Replacing the ball is a pain but often easier than replacing the entire valve. Here is a source for the rebuild kit: 272742A - Honeywell 272742A - Ball & O-Ring for Zone Valve
    Thanks so much for the response and the link. I checked the connections on the thermostat - all tight - and working.
    I gave the valve some good bangs with a hammer - flow stopped - pipes went cool... so I'm guessing it was stuck - it hasn't been exercised for many months.
    I will exercise this zone more frequently and hope it continues to function but realize I mighjt be on borrowed time with the valve.

    Thanks again
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #4

    Dec 14, 2014, 11:14 AM
    Something I do, probably overkill but I never have water flow problems, is to exercise each zone once a week, all year long. Simply turn up each stat until you can feel the pipes get warm then shut it down. Takes all of 5 minutes.
    Russ1111's Avatar
    Russ1111 Posts: 3, Reputation: 1
    New Member
     
    #5

    Dec 14, 2014, 02:54 PM
    Quote Originally Posted by Grady White View Post
    Something I do, probably overkill but I never have water flow problems, is to exercise each zone once a week, all year long. Simply turn up each stat until you can feel the pipes get warm then shut it down. Takes all of 5 minutes.
    Yes - called for heat and then shut it down again today - working normally. Lesson learned I think.

    Thank you for your feedback!
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #6

    Dec 14, 2014, 03:34 PM
    If nothing else, it will let you know of a problem before the heating season sets in. Certainly worth the little bit of time it takes & the cost of a few long dead dinasours.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Taco zone valve 571-2. Water flow not like the arrow in the valve's body. [ 0 Answers ]

I had a Taco zone valve 571-2 installed recently. Later I noticed that the valve is installed with the arrow in body of the valve pointing to the opposite direction of the actual water flow. I called the plumber and he said that this is not a problem and no damage will occur to the valve, the...

I have a weil-mclain boiler. The zone valve opens but no heat in zone. What do I do? [ 1 Answers ]

Have replaced the zone valve actuator, but it doesn't seem to be fixing the problem. What else can I do?

Zone valve parts [ 3 Answers ]

The shutoff ball inside my zone valve fell apart. Are parts loke that available

Zone valve problem [ 5 Answers ]

Zone valve for upstairs will not open. Already replaced thermostat. The only time I have heat upstairs is when the valve in manually opened and the downstairs heat kicks on. Any help or advice would be great! Thank you.

Zone valve [ 1 Answers ]

Got a white rogers zone valve spinning and not stopping ,has my end switch burned out .


View more questions Search