    York diamond 90 gas furnace
    Furnace code in 3 pressure switch stuck open should I replace switch
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Dec 2, 2013, 08:10 AM
    The switches do fail. However, make sure all the orifices are open and not clogged with debris. `Remove the hoses and carefully clean them out with a paper clip.
    sam1962's Avatar
    sam1962 Posts: 3, Reputation: 1
    New Member
     
    #3

    Dec 2, 2013, 01:00 PM
    Quote Originally Posted by ma0641 View Post
    The switches do fail. However, make sure all the orifices are open and not clogged with debris. `Remove the hoses and carefully clean them out with a paper clip.
    thanks for the tip. I've done that and I cleaned and checked a number of related parts. It was working for a while ,then would 'nt fire. The vent and blower motors are working , ignitor glows and sometimes fires. The controler then blinks 3times by the chart it means pressure switch stuck open. Do you think the switch is gone or could it be??
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #4

    Dec 2, 2013, 02:58 PM
    I would make sure to clean the flame sensor using fine sandpaper or steel wool. Pressure switches are relatively inexpensive and easy to replace. You can test it by measuring voltage across the terminals when the induced fan is running and calling for heat. Should show 24 volts Dc or AC depending on heater. You can Aldo test jump the terminals and try the heater. If it starts and runs replace the switch.
    sam1962's Avatar
    sam1962 Posts: 3, Reputation: 1
    New Member
     
    #5

    Dec 2, 2013, 06:27 PM
    Quote Originally Posted by ma0641 View Post
    I would make sure to clean the flame sensor using fine sandpaper or steel wool. Pressure switches are relatively inexpensive and easy to replace. You can test it by measuring voltage across the terminals when the induced fan is running and calling for heat. Should show 24 volts Dc or AC depending on heater. You can Aldo test jump the terminals and try the heater. If it starts and runs replace the switch.
    O.k I'll try to test and jump.the sensor looked clean but ill take some emery cloth to itand see what happens. Thanks again.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #6

    Dec 2, 2013, 08:52 PM
    Quote Originally Posted by sam1962 View Post
    O.k I'll try to test and jump.the sensor looked clean but ill take some emery cloth to itand see what happens. Thanks again.
    DO NOT use emory cloth. Scotch brite pad or fine steel wool only. Emory & some sandpaper will leave permanent scratches which can & do cause either damage or excessive deposits.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

York Diamond 90 Furnace [ 1 Answers ]

White Rodgers Emerson 50a50-241, blower fan come on for 10 second and shut off. led flash 4 time. What can be the cause for the led to flash 4 time?

York diamond 80 gas furnace heats but blower stays on continuously [ 5 Answers ]

York Diamond 80 mid efficiency gas furnace. Has worked OK up to last night. Main blower will not shut off, it runs continuously. When heat is called for, all works well. When set temp is reached, gas shuts off, but blower continues. I removed blower door, blower turns off via the door switch. ...

York Diamond 80 Furnace [ 0 Answers ]

My furnace will come on it if I hit the circuit breaker. After that it never comes back on. Anyone know what is wrong or what I should try? I have turned it off and did the basic things but nothing happens. Help! Kurt

York Diamond 80 Gas furnace (main blower stopped in 2 minutes and never come back) [ 2 Answers ]

I inspected the furnace and found it starts normally (frame, main blower, another motor on top of furnace... etc.) initial time but main blower stopped after 2 -3 minutes even though frame (fire) is on. Frame went out 1-2 minutes after main blower stopped. Frame is continuing to on and off but...


View more questions Search