Ask Experts Questions for FREE Help !
Ask
    Michael K404's Avatar
    Michael K404 Posts: 2, Reputation: 1
    New Member
     
    #1

    Aug 3, 2012, 07:21 AM
    PVC Conduit Body
    Within a 1/2 in PVC conduit body there is 4 cu in of space. When applying the wire volume rules to conductors entering this body it seems that this size body is not very useful. For example, if I were to use #12 wire (volume = 2.25) I would only be allowed to have 1 conductor entering the body, because it's only 4 cu in.

    Have I gone wrong in this calculation?
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Aug 3, 2012, 09:49 AM
    Mike,
    If you are not splicing in the conduit body then the maximum number of conductors is maximum number permitted by table 1 or chapter 9 for the conduit or tubing to which it is attached...
    If you are splicing then use 314.16(C)(2).
    Michael K404's Avatar
    Michael K404 Posts: 2, Reputation: 1
    New Member
     
    #3

    Aug 4, 2012, 07:29 AM
    Quote Originally Posted by hfcarson View Post
    Mike,
    If you are not splicing in the conduit body then the maximum number of conductors is maximum number permitted by table 1 or chapter 9 for the conduit or tubing to which it is attached...
    If you are splicing then use 314.16(C)(2).
    I will not be splicing. Thank you very much. That makes sense. It's just the answer I wanted to hear.

    I'll be using #12 THHN in 1/2" sch 40 PVC and it looks like 8 conductors are permitted. More than I want.

    I'm grateful that you're here for us.
    Michael
    shuntripper's Avatar
    shuntripper Posts: 180, Reputation: 8
    Junior Member
     
    #4

    Aug 4, 2012, 08:10 AM
    8 are max fill, but more than 5 and you have to derate them

    Just sayin'
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #5

    Aug 4, 2012, 08:17 AM
    Shunt...
    More than 3 and you have to derate..
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #6

    Aug 4, 2012, 08:25 AM
    More specifically... more than 3 "current carrying conductors"...

    In this case with #12 AWG THHN 90C copper, (most likely),
    Eight #12 derate to 70% which would be 21 amps... 12 AWG is required
    To be protected by a 20 ampere overcurrent so here the derating is somewhat
    Of non-issue...

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Romex in PVC Conduit ? [ 26 Answers ]

Need to run #12 wire to my gate opener. Have 1" schedule 80 conduit in ground. Can I run 12/2 Romex through the conduit to feed the gate ? Or do I have to run individual wires. Thank You

Running romex in pvc conduit? [ 3 Answers ]

Washington mentioned THHN or UF for outdoor use. Did he then mean UF can be run in conduit? I am wanting to put two runs of 12/3 inside conduit running underneath a deck to a hot tub. They are 240V circuits at 20A and 30A. The run is about 50 ft which sounds like 12 ga copper should work. I...

12/2 NM-B Romex in PVC Conduit [ 4 Answers ]

Hi. I need to bring 2 new circuits from the panel in the garage to the basement. I would like to use 12/2 NM-B (Romex with ground) from the panel through PVC conduit to the basement. It is about a 12' run, then a 90 degree turn, then about another 10' to a spot below the panel. At this point it...

How to pull #12 through 3/4 pvc conduit [ 15 Answers ]

How is the best way to pull a #12 neutral and #12 ground insulated through 3/4 pvc conduit that already has 2 #12 black wires. I need to get rid of one of the black wires and replace it with the white neutral and green ground. It has at least 3 90 degree ells.

Painting PVC electrical conduit. [ 2 Answers ]

I am trying to paint gray pvc electrical conduit to match the color of the house. The house is painted with BEHR self-priming acrylic latex house paint for masonry, stucco, & brick. Is there a special primer for this project?:confused:


View more questions Search