    Circuit breaker
    On a THIN double 30 amp GE breaker, there is a metal piece protruding out the bottom that prevents it from inserting into panel. Does removing this piece affect the effectiveness of the breaker??
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Jun 6, 2012, 03:03 PM
    Are you sure the breaker is approved for the panel box? Sounds like the wrong breaker. What brand is the box? What brand is the breaker? Does this breaker have the same classification as the other breakers?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Jun 7, 2012, 02:37 AM
    Do not remove the metal tab found on the bottom of the GE # THQP circuit breakers. It is there to limit the types of panels it is allowed to be installed into.
    wintergreen74's Avatar
    wintergreen74 Posts: 4, Reputation: 1
    New Member
     
    #4

    Jun 7, 2012, 06:56 AM
    Quote Originally Posted by tkrussell View Post
    Do not remove the metal tab found on the bottom of the GE # THQP circuit breakers. It is there to limit the types of panels it is allowed to be installed into.

    Thank you for your reply. The box is GE and the breaker is a GE. The large double breaker has metal tabs that fit into the box 'horizontal' while the THIN has tabs that fit 'vertical'. The box does allow for either, but does not want to seat tightly.
    wintergreen74's Avatar
    wintergreen74 Posts: 4, Reputation: 1
    New Member
     
    #5

    Jun 7, 2012, 07:02 AM
    Quote Originally Posted by ma0641 View Post
    Are you sure the breaker is approved for the panel box? Sounds like the wrong breaker. What brand is the box? What brand is the breaker? Does this breaker have the same classification as the other breakers?

    Thank you for your reply. The box is GE and the breaker is a GE. The large double breaker has metal tabs that fit into the box 'horizontal' while the THIN has tabs that fit 'vertical'. The box does allow for either, but does not want to seat tightly but it does work.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Jun 7, 2012, 07:27 AM
    If THQP breakers are allowed in the panel, it will be listed on the label found on the inside of the panel door, and the label will have a diagram to show exactly which slots can accept the THQP breakers.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #7

    Jun 7, 2012, 07:39 AM
    Some spaces on the buss may allow that breaker, but as TK mentions, it limits the amount of them.
    wintergreen74's Avatar
    wintergreen74 Posts: 4, Reputation: 1
    New Member
     
    #8

    Jun 7, 2012, 04:23 PM
    Quote Originally Posted by tkrussell View Post
    If THQP breakers are allowed in the panel, it will be listed on the label found on the inside of the panel door, and the label will have a diagram to show exactly which slots can accept the THQP breakers.
    Thanks for your reply. I will check the door panel.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Theory of vacuum Circuit Breaker & sf6 circuit breaker [ 15 Answers ]

I want to know about the basic Theory of vacuum Circuit Breaker & sf6 circuit breaker

Why vacuum circuit breaker is prefer on oil circuit breaker ? [ 1 Answers ]

Why vacuum circuit breaker is prefer on oil circuit breaker ?

I have a Murray circuit breaker panel and want to add a circuit for a 3 prong elec dr [ 3 Answers ]

I have an electric 3 pronged dryer that I want to add a circuit for on my Murray Circuit Panel. What kind of switch do I need?

Circuit Breaker trips because two bathrooms and master bedroom on same circuit [ 6 Answers ]

Some electrician committed a blunder in my opinion about 17 years ago. The master bedroom and two full bathrooms are all on the same circuit. If two hair dryers are used at the same time, it will trip the breaker every time. In figuring out what amperage would be required for two hair dryers and...


View more questions Search