    National electric code free online?
    Is double tapping permitted when joining 2 conductors of the same gauge into a Square D QO type breaker
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Jun 4, 2011, 04:06 PM

    No, you may not double tap a circuit breaker. (you do mean attaching two hot conductors to the same breaker, don't you?)

    Apart from the NEC, it may also be prohibited by the manufacturer. It the CB has been listed as a single conductor device, UL has only listed it for that connection.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Jun 4, 2011, 06:07 PM
    Don, please check your facts on this one.

    The term "double tap" is not any kind of official term. This is a term made up by home inspectors.

    There is no prohibition in the NEC to put two conductors on a breaker if that breaker is designed to accept two conductors.

    Square D QO and HOM (15, 30 & 30 amp) are both designed to accept two conductors of the same size.
    Many Cutler Hammer CH series are this way as well.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Jun 4, 2011, 06:20 PM

    Stan, that's what I said.

    Apart from the NEC, it may also be prohibited by the manufacturer. If the CB has been listed as a single conductor device, UL has only listed it for that connection."
    "
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Jun 4, 2011, 06:42 PM
    Quote Originally Posted by donf View Post
    No, you may not double tap a circuit breaker. (you do mean attaching two hot conductors to the same breaker, don't you?)

    Apart from the NEC, it may also be prohibited by the manufacturer.
    Oh, I was going more by this, which the way I read it is saying: "No, you may not double tap a circuit breaker.".
    The second sentence I thought you meant along with the NEC prohibiting it...

    OK then. :)

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

National electric code free online [ 6 Answers ]

I need to install a lit exit sign in a 759 sq ft. office. The door that I am putting this unit above is located far from the other already installed exit sign and would require going through a block wall at an added expense to the customer. Will the code allow me to connect the sign to an...

National electric code free online [ 16 Answers ]

What's the distance for gfci from water fixture?

National electric code free online [ 4 Answers ]

What size J box do I need? I have 2 -2 1/2 " emt conduits coming in with 4 250 mcm conductors?

National electric code free online [ 2 Answers ]

Are insulated recess housings required on the first floor of a two story residence if the first floor ceiling is not insulated?

National electric code free online [ 2 Answers ]

Outdoor uplighting requirements for low voltage and 120v?


View more questions Search