    I have a 3 1/2 ton aman system and I have had a problem cooling the house when it hot outside.(over 90)'

    It cools perfectly fine when the temperature is in the 80's. I checked the evap. Coil and it looks very clean. So is the condenser. The suction line and head reads 74/220. Temp at register is 64 and temp at return is 76.

    I had the ducts checked and tey where all sealed properly with no leaks. The repair man said it just the hot heat but I didn't have this issue last year. The home is 1500Sq foot and has about 18inches of insulation in the attic.

    I can't figure out what is wrong and neither can the AC techs. I have a newborn and want to get this solved as soon as poosble without having to keep calling technicians out. I had two different ones come out and still having te same issue :(
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    Jun 5, 2010, 04:41 PM

    1500 sf only takes a 2 ton unit you are probably not getting any humidity out of the house. Is this how old is this system? Are the registars in the floor or the celing?
    cibarra's Avatar
    cibarra Posts: 11, Reputation: 1
    New Member
     
    #3

    Jun 6, 2010, 09:35 AM
    Quote Originally Posted by Joshdta View Post
    1500 sf only takes a 2 ton unit you are probally not getting any humidity out of the house. Is this how old is this system? are the registars in the floor or the celing?



    The are in the ceiling all 8' except living room has vaulted ceilings. The system is the original size the home came with and had never had any problems up to this year. The condenser was changed 3 years ago but the air handler inside is about 9 years old but the coil is clean as a whistle
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #4

    Jun 6, 2010, 10:02 AM

    Sounds like you then have a 13 seer outdoor unit and a 10 seer coil inside, did they make any modifications to the indoor unit when the outdoor was changed?
    cibarra's Avatar
    cibarra Posts: 11, Reputation: 1
    New Member
     
    #5

    Jun 6, 2010, 02:59 PM
    Quote Originally Posted by Joshdta View Post
    sounds like you then have a 13 seer outdoor unit and a 10 seer coil inside, did they make any modifications to the indoor unit when the outdoor was changed?
    No I don't believe so. But it worked fine up to now! Should I just suck it up and replace the inside air handler?

    Today it didn't go below 82 but last night I had to adjust the thermostat because it got too cold(72)
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Jun 6, 2010, 03:56 PM
    Temp at register is 64 and temp at return is 76

    You only have a 12 degree TD and it should be 18 to 20.

    Many things can cause this.

    If your indoor coil is a 10 SEER and the outside unit is a 13 SEER they should have installed an expansion valve.

    If the unit has been opened lately or refrigerant added the system could have noncondensibles. The only way to find that out is to recover the refrigerant from the system and recharge with fresh/pure refrigernat of known quality.

    The refrigerant charge can be a challenge on these mixed units. I would check the subcooling AND the superheat and see what category it is falling into. This might tell you if you are over charged/under charged.

    There are many more items that could be causeing this but a knowledgeable person would actually have to give it a good look over.

    I assume this is a R-22 machine but you never stated the refrigerant type.

    Somewhere in your area there is a HVAC person with enough talent to correct your problems. The problem will be to find that person.
    cibarra's Avatar
    cibarra Posts: 11, Reputation: 1
    New Member
     
    #7

    Jun 6, 2010, 10:55 PM
    Quote Originally Posted by hvac1000 View Post
    Temp at register is 64 and temp at return is 76

    You only have a 12 degree TD and it should be 18 to 20.

    Many things can cause this.

    If your indoor coil is a 10 SEER and the outside unit is a 13 SEER they should have installed an expansion valve.

    If the unit has been opened lately or refrigerant added the system could have noncondensibles. The only way to find that out is to recover the refrigerant from the system and recharge with fresh/pure refrigernat of known quality.

    The refrigerant charge can be a challenge on these mixed units. I would check the subcooling AND the superheat and see wat catagory it is falling into. This might tell you if you are over charged/under charged.

    There are many more items that could be causeing this but a knowledgeable person would actually have to give it a good look over.

    I assume this is a R-22 machine but you never stated the refrigerant type.

    Somewhere in your area there is a HVAC person with enough talent to correct your problems. The problem will be to find that person.
    It is a R-22 unit and the refrigerant was recovered just last week and new one put it. Also it does have an expansion valve and the tech told me it was working fine. He said the suction line would either read nothing or very high if this was the problem.

    I have one more tech coming out in the next couple if days. He will be the third hopefully he can fix it.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

My grandmother was born in england... I was born in the usa and now moving to london [ 1 Answers ]

My grandmother was born in england... I just bought flat in London... am I eligible for british citizenship?

Maytag freezer is cooling... fridge is not cooling. Any suggestions? [ 0 Answers ]

Maytag refridge is not cooling (freezer is). Any suggestions or does anyone know if I need a repair person and what the problems and range of expected reasonable costs might be to have it fixed.

Why would my downstairs shower not be getting very hot and cooling off quickly? [ 0 Answers ]

All other sinks (kitchen/half bath sink) get VERY hot and stay hot. Master bath shower has to be all the way on hot and then is still not that hot and seems to cool off quickly. Fixture is a single turn handle type.

Can I claim my new born child that was born on January 2008 [ 3 Answers ]

Can I claim my new born child born in January 2008 on my 2007 taxes?


View more questions Search