    20 amp circuit breaker
    My electric dryer is connected to a dedicated 20 Amp, 240 V circuit breaker. Recently this breaker has begun triping. Thinking it was a faulty dryer, I replaced the dryer but the breaker continues to trip.

    The breaker panel was installed when the home was built in the mid 1960s.
    Can breakers become fatigued with time? If so, can the breaker be re-calibrated or does it need to be replaced?

    The breaker panel name plate reads:
    Pushmatic
    Electri-Center
    Bulldog Products Division


    I've looked for a breaker replacement in home improvement stores and nothing looks a direct replacement.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    May 6, 2010, 10:43 AM

    Most dryers now are ran on 10 gage wire and 30 amp breaker
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #3

    May 6, 2010, 07:58 PM
    Sounds like you have a couple of problems. The new dryer probably requires a 30 amp circuit, and you only have a 20. The real issue is that if you have a 20 amp cicuit now, the wiring you have is not large enough to handle a 30 amp breaker. You will need to replace the wiring from the breaker panel to the dryer outlet... and also the breaker.
    creahands's Avatar
    creahands Posts: 2,854, Reputation: 195
    Ultra Member
     
    #4

    May 7, 2010, 01:22 AM

    U will probably have to go to an electrical supply house to get the breaker.

    Chuck
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #5

    May 7, 2010, 04:22 AM

    Home Depot claims to carry Pushmatic breakers.
    See this site
    ADVASI's Avatar
    ADVASI Posts: 2, Reputation: 1
    New Member
     
    #6

    May 7, 2010, 10:33 AM
    Quote Originally Posted by Missouri Bound View Post
    Sounds like you have a couple of problems. The new dryer probably requires a 30 amp circuit, and you only have a 20. The real issue is that if you have a 20 amp cicuit now, the wiring you have is not large enough to handle a 30 amp breaker. You will need to replace the wiring from the breaker panel to the dryer outlet....and also the breaker.
    Thanks Missouri Bound,
    I think you nailed my problem. The new Dryer installation docs. Call for a dedicated 30Amp circuit. I wasn't aware since I've used the 20Amp circuit for about 19 years w/o a problem.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #7

    May 7, 2010, 01:46 PM
    Your welcome, and best of luck

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Theory of vacuum Circuit Breaker & sf6 circuit breaker [ 15 Answers ]

I want to know about the basic Theory of vacuum Circuit Breaker & sf6 circuit breaker

15 amp duplex recept on 20 amp circuit breaker [ 2 Answers ]

Can you put in 15 amp outlets that has 12 gauge wire on a 20 amp circuits these are just regular household outlets not used for dryers or refrigerator. Or should I replace with 20 amp outlets.

20 amp circuit breaker [ 7 Answers ]

I recently had a new pump 1 1/2 hp installed for my sprinkler system which replgaced a 1hp. It was connected to a 15 amp circuit. With the new pump, the breaker kept popping. It was suggested to change this to a 20 amp. We did, using an electrician.(there is a label on the pump that says max...

Replacing Circuit Breaker with Higher AMP Breaker [ 8 Answers ]

Excuse me, I did look at the code book as is suggested in your Sticky. The NFPA may answer this question, but I am not knowledgeable enough to recognize it: Our offices are upstairs in an older (renovated home) building with modern wiring. We have 4 computers, 3 printers, and miscellaneous with...


View more questions Search