    toddhoppe's Avatar
    toddhoppe Posts: 3, Reputation: 1
    New Member
     
    #1

    Apr 26, 2010, 05:20 PM
    heat but no ac
    I replaced my thermostat, when I turned the power on ,nothing . I found I hs=ad blown a 3 amp fuse by the transformer because I wired the thermostat wrong. The heat now works but not the ac, is there another fuse for that . It's a york model p3huc20n09201c
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    Apr 26, 2010, 06:05 PM

    No there is no other fuse. Do you have a jumper from rh to rc??
    toddhoppe's Avatar
    toddhoppe Posts: 3, Reputation: 1
    New Member
     
    #3

    Apr 26, 2010, 06:30 PM

    no my last therm had w=w, r=r, y=y, g=g , blue=c, I didn't think I needed the jumper because the old one didn't, 'do I '?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #4

    Apr 26, 2010, 06:34 PM

    If there is no red wire on rc you will not send power to the ac unit. So a jumper must be installed if your new stat has both a rh and rc. I think this will take care of your problem. Make sure to turn off power on furnace before installing the jumper.
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #5

    Apr 26, 2010, 06:44 PM
    Quote Originally Posted by toddhoppe View Post
    i replaced my thermostat, when i turned the power on ,nothing . i found i hs=ad blown a 3 amp fuse by the transformer because i wired the thermostat wrong. the heat now works but not the ac, is there another fuse for that . its a york model p3huc20n09201c
    You/everyone should always kill the power to furnace before installing new tstat or doing anything to the low voltage wiring / or high voltage wires
    toddhoppe's Avatar
    toddhoppe Posts: 3, Reputation: 1
    New Member
     
    #6

    Apr 27, 2010, 11:23 AM

    thanks joshdta, I jumped rc=rh and it works, just in time for so-cal heat!
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #7

    Apr 27, 2010, 12:42 PM

    Great glad it is working for you

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heat pump never turns on, handler blows continuous with no heat except with AUX heat [ 2 Answers ]

10 year old Rheem air handler RHBA-21J8MFCA, 1/3HP, 2.8A. New WeSt Columbia, SC 29170, Model 2HP13L48P-1B, HCFC-22, 4TON. Installed new out of box iN July and AC working splendidly but start-up is "violent" and loud. Installer says I need some sort of "start-up kit". I put off as had planned...

Heat Pump blows 5amp fuse when switching between defrost & back to heat. Them Heat work [ 3 Answers ]

I have a Carrier Heat Pump System. It’s about 5 years old and has functioned OK until this Christmas Eve. One problem is the condensing unit is not kicking back on after it goes into defrost mode. I found a 5AMP fuse blown in the attic unit and once replaced it functioned. At least for a day or two...

Is a heat pump with emergency heat a multi stage heat pump [ 1 Answers ]

I am trying to replace the thermostat for my heat pump the one I've got seems to be running the emergency heat only. All wires were connected as they were in the old one. Is regular heat and emergency heat considered multi-stage? If so, I need another thermostat... please advise.

Carrier Hvac heat pump with aux/em heat- NO AUX HEAT [ 1 Answers ]

I have tried to install Honeywell 7500d thermostat. I get heat pump heat but no emergency heat although the termostate is calling for it. The installation manual says to see authorized agent if I have a dual 0/b on existing thermostat and another wire is attached to common. As of now, I have ...


View more questions Search