    wire honeywell thermostat in trane xe1200
    I have a trane xe1200 with original weathertron thermostat.I bought a honeywell pro 3000 digital,2 heat/1 cool.I need to know what wires go where.the wires on the weathertron are o=orange,g=green,y=yellow,x2=black,b=blue,t=brown, r=red,w=white.honeywell model number is th3210d1012.any help would be much appreciated
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    May 16, 2009, 02:15 PM

    what are the termanal on the honeywell?

    o-orange
    r-red jumped to rc
    g-green
    c-blue
    x or l-black
    aux-white
    w2- brown jumped to e
    y-yellow
    mwknitro's Avatar
    mwknitro Posts: 12, Reputation: 1
    New Member
     
    #3

    May 16, 2009, 02:24 PM

    The terminals are, e-aux-y-g-o-l-r-b-c
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #4

    May 16, 2009, 02:27 PM

    The wiring I just gave you should work fine. The only one I am not 100% positive is the brown wire you have on t now. Can you look down stairs at your blower and see what the brown is hooked to?
    mwknitro's Avatar
    mwknitro Posts: 12, Reputation: 1
    New Member
     
    #5

    May 16, 2009, 02:39 PM

    I don't want to mess this up,I have already blown a fuse and I am not clear on what you are telling me,like where e,l,c goes to.could you respond stating each letter,and what color wire to hook up to it.I can go under the house and try to see what brown is hooked to if needed.thanks for your time
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #6

    May 16, 2009, 02:51 PM

    Black goes on L
    Blue on C
    And e is emergency heat, that will probably be your brown wire.
    mwknitro's Avatar
    mwknitro Posts: 12, Reputation: 1
    New Member
     
    #7

    May 16, 2009, 03:04 PM
    Thanks a lot,I will hook it up.
    mwknitro's Avatar
    mwknitro Posts: 12, Reputation: 1
    New Member
     
    #8

    May 16, 2009, 07:40 PM
    Hooked it up and air worked fine.switched to heat and it worked fine,seems to.switched to emergency heat and it kept running.switched back to regular heat while it was running and it blew the 5 amp fuse under house.instructions said may have to put a jumper between e and aux if it has no relay.think that might fix that,or did I just switch heat too quickly.had also posted about wiring thermostat on fixya.com,and someone wrote that this thermostat would not work for this unit,but I bought the 2 heat/1 cool,not the one heat one cool,and I bought from trane dealer<salesperson>what do you think,you got me this far,and I really appreciate it.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #9

    May 16, 2009, 07:41 PM

    We still need to know what the bron wire is hooked to under the house to make sure it is wired right.
    mwknitro's Avatar
    mwknitro Posts: 12, Reputation: 1
    New Member
     
    #10

    May 16, 2009, 07:54 PM
    The wires that come from the thermostat go to the outside unit,where the condenser fan is.is that where I need to look?sorry if I am a little slow,had a busy day.if so I will take the cover off and look
    mwknitro's Avatar
    mwknitro Posts: 12, Reputation: 1
    New Member
     
    #11

    May 16, 2009, 08:05 PM
    Quote Originally Posted by mwknitro View Post
    the wires that come from the thermostat go to the outside unit,where the condenser fan is.is that where i need to look?sorry if i am a little slow,had a busy day.if so i will take the cover off and look
    it is pouring rain.I was going to go look anyway,will do tomorrow,and let you know
    mwknitro's Avatar
    mwknitro Posts: 12, Reputation: 1
    New Member
     
    #12

    May 17, 2009, 10:13 AM

    I looked under the house where wires coming in at blower, and color brown was wired together going to outside unit.it is hooked to the small circuit board on outside unit,and the terminal on board is marked t1.also,don't know if it matters,there is a small 24 volt,some type of solenoid on outside unit,and at the time I checked for wire it was making a slight humming noise.may be normal,I don't know.just thought I would ask.would like to be done wiyh this,thanks again
    mwknitro's Avatar
    mwknitro Posts: 12, Reputation: 1
    New Member
     
    #13

    May 17, 2009, 11:56 AM
    Quote Originally Posted by mwknitro View Post
    i looked under the house where wires coming in at blower, and color brown was wired together going to outside unit.it is hooked to the small circuit board on outside unit,and the terminal on board is marked t1.also,dont know if it matters,there is a small 24 volt,some type of solenoid on outside unit,and at the time i checked for wire it was making a slight humming noise.may be normal,i dont know.just thought i would ask.would like to be done with this,thanks again
    It is the defroster board I think
    mwknitro's Avatar
    mwknitro Posts: 12, Reputation: 1
    New Member
     
    #14

    May 17, 2009, 11:57 AM
    [QUOTE=mwknitro;1740687]it
    mwknitro's Avatar
    mwknitro Posts: 12, Reputation: 1
    New Member
     
    #15

    May 17, 2009, 01:40 PM

    I found the brown wire.it goes to the outside unit and is hooked to a small circuit board.marked t1.from what I have read its maybe a wire for thermistor?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #16

    May 17, 2009, 04:30 PM

    This brown wire probably needs to be on aux insteed of white. But with out the wiring diagram from your units I can not say for sure. But I am still trying to figure out what blew the fuse this time. Have the brown on e should not have blown it.
    mwknitro's Avatar
    mwknitro Posts: 12, Reputation: 1
    New Member
     
    #17

    May 18, 2009, 12:07 PM

    Brown is not used,and black goes to e,to let you know

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Trane to Honeywell Thermostat (4 wire)? [ 11 Answers ]

I have been trying for days to get my Honeywell RTH-221b Thermostat to work with my AC. It's been working all winter for Heat, but now when I need it for cooling it does not work. I was able to take some pics of the old and new wiring. This is the old wiring: ...

Loud noise from my Trane XE1200 [ 1 Answers ]

Hello everyone, I woke up this morning to my Trane xe1200 making a loud knocking noise while it was running. I know next to nothing about heating and cooling and I am concerned since I haven't heard it making this much noise before. I live in Texas and it was the coldest night we have had so...

How do Ichange from trane thermostat 3AAT80B1A1 two stage to a honeywell Th321OD wire [ 1 Answers ]

I need a wiring diagram of the trane Thermostat

Switching from Trane (6-wire) to Honeywell (5-wire) [ 6 Answers ]

I am wanting to change from a Trane tstat (model TAYSTAT241) with six wires: Green to G1, Red to R, Blue to B, White to W1, Brown to W2, and yellow to Y1 to a Honeywell Programmable (RTH230B) with five connections: Rh to Rc (jumped), W, Y, G. I have a Trane XV90 (model # TXC031C4HPCO-1999). My...