  • May 16, 2009, 12:28 PM
    mwknitro
    wire honeywell thermostat in trane xe1200
    I have a trane xe1200 with original weathertron thermostat.I bought a honeywell pro 3000 digital,2 heat/1 cool.I need to know what wires go where.the wires on the weathertron are o=orange,g=green,y=yellow,x2=black,b=blue,t=brown, r=red,w=white.honeywell model number is th3210d1012.any help would be much appreciated
  • May 16, 2009, 02:15 PM
    Joshdta

    what are the termanal on the honeywell?

    o-orange
    r-red jumped to rc
    g-green
    c-blue
    x or l-black
    aux-white
    w2- brown jumped to e
    y-yellow
  • May 16, 2009, 02:24 PM
    mwknitro

    The terminals are, e-aux-y-g-o-l-r-b-c
  • May 16, 2009, 02:27 PM
    Joshdta

    The wiring I just gave you should work fine. The only one I am not 100% positive is the brown wire you have on t now. Can you look down stairs at your blower and see what the brown is hooked to?
  • May 16, 2009, 02:39 PM
    mwknitro

    I don't want to mess this up,I have already blown a fuse and I am not clear on what you are telling me,like where e,l,c goes to.could you respond stating each letter,and what color wire to hook up to it.I can go under the house and try to see what brown is hooked to if needed.thanks for your time
  • May 16, 2009, 02:51 PM
    Joshdta

    Black goes on L
    Blue on C
    And e is emergency heat, that will probably be your brown wire.
  • May 16, 2009, 03:04 PM
    mwknitro
    Thanks a lot,I will hook it up.
  • May 16, 2009, 07:40 PM
    mwknitro
    Hooked it up and air worked fine.switched to heat and it worked fine,seems to.switched to emergency heat and it kept running.switched back to regular heat while it was running and it blew the 5 amp fuse under house.instructions said may have to put a jumper between e and aux if it has no relay.think that might fix that,or did I just switch heat too quickly.had also posted about wiring thermostat on fixya.com,and someone wrote that this thermostat would not work for this unit,but I bought the 2 heat/1 cool,not the one heat one cool,and I bought from trane dealer<salesperson>what do you think,you got me this far,and I really appreciate it.
  • May 16, 2009, 07:41 PM
    Joshdta

    We still need to know what the bron wire is hooked to under the house to make sure it is wired right.
  • May 16, 2009, 07:54 PM
    mwknitro
    The wires that come from the thermostat go to the outside unit,where the condenser fan is.is that where I need to look?sorry if I am a little slow,had a busy day.if so I will take the cover off and look
  • May 16, 2009, 08:05 PM
    mwknitro
    Quote:

    Originally Posted by mwknitro View Post
    the wires that come from the thermostat go to the outside unit,where the condenser fan is.is that where i need to look?sorry if i am a little slow,had a busy day.if so i will take the cover off and look

    it is pouring rain.I was going to go look anyway,will do tomorrow,and let you know
  • May 17, 2009, 10:13 AM
    mwknitro

    I looked under the house where wires coming in at blower, and color brown was wired together going to outside unit.it is hooked to the small circuit board on outside unit,and the terminal on board is marked t1.also,don't know if it matters,there is a small 24 volt,some type of solenoid on outside unit,and at the time I checked for wire it was making a slight humming noise.may be normal,I don't know.just thought I would ask.would like to be done wiyh this,thanks again
  • May 17, 2009, 11:56 AM
    mwknitro
    Quote:

    Originally Posted by mwknitro View Post
    i looked under the house where wires coming in at blower, and color brown was wired together going to outside unit.it is hooked to the small circuit board on outside unit,and the terminal on board is marked t1.also,dont know if it matters,there is a small 24 volt,some type of solenoid on outside unit,and at the time i checked for wire it was making a slight humming noise.may be normal,i dont know.just thought i would ask.would like to be done with this,thanks again

    It is the defroster board I think
  • May 17, 2009, 11:57 AM
    mwknitro
    [QUOTE=mwknitro;1740687]it
  • May 17, 2009, 01:40 PM
    mwknitro

    I found the brown wire.it goes to the outside unit and is hooked to a small circuit board.marked t1.from what I have read its maybe a wire for thermistor?
  • May 17, 2009, 04:30 PM
    Joshdta

    This brown wire probably needs to be on aux insteed of white. But with out the wiring diagram from your units I can not say for sure. But I am still trying to figure out what blew the fuse this time. Have the brown on e should not have blown it.
  • May 18, 2009, 12:07 PM
    mwknitro

    Brown is not used,and black goes to e,to let you know