    Tempstar SP80 w/SV9500. No pilot.
    Woke up a little frosty this morning.
    Furnace is blowing, but no heat.
    I pulled the top cover on the SP80 and witnessed the startup sequence.
    I see no glow from the smart valve ignoter/flame rod assembly (Q3400) and the pilot never lights. The small motor/fan that gets air flow going is running, and I threw my multimeter across the nearby vacuum switch and it reads open before the fan starts and open once the small motor is engaged.

    I'm leaning towards either a bad igniter element or a faulty SV9500 valve.
    Can someone help me with the troubleshooting process from this point onward?

    Should I read 24VDC across the 2 blue wires to the igniter a few seconds into the ignition sequence?

    I've heard about faulty solder joints in the SV9500/9501 series smart valves, and temporary fixes of wedging a shim near the connector. Which way do you push the connector? I was a certified electronic technician years ago and am good with a soldering gun, can the bad connection in the SV9500 be repaired?

    Help! It's cold in here!
    Spiff59's Avatar
    Spiff59 Posts: 5, Reputation: 1
    New Member
     
    #2

    Jan 31, 2009, 10:08 AM

    Pardon, the vacuum switch reads closed after the small fan begins to run. (I don't see that I can edit my original post here?)
    greghvacguy's Avatar
    greghvacguy Posts: 45, Reputation: 2
    Junior Member
     
    #3

    Jan 31, 2009, 10:30 AM

    If your getting a glow you should be getting gas to the pilot. If not check to see if your pilot need to be cleaned. On your gas vaule does the wires come in to top or is one on the side. If you have one on the side yes they have bad connection try and to wiggel it.I Don't Recommend ON FIXING ANY GAS VAULE GET NEW ONE.
    Sounds like your proplem is in pilot or gas.
    Hope this helps
    Spiff59's Avatar
    Spiff59 Posts: 5, Reputation: 1
    New Member
     
    #4

    Jan 31, 2009, 10:56 AM
    Quote Originally Posted by greghvacguy View Post
    If your getting a glow you sould be getting gas to the pilot. If not check to see if your pilot need to be cleaned. on your gas vaule does the wires come in to top or is one on the side. If you have one on the side yes thay have bad connection try and to wiggel it.I DONT RECOMEND ON FIXING ANY GAS VAULE GET NEW ONE.
    sounds like your proplem is in pilot or gas.
    hope this helps
    Nope, no glow. I pulled the connector to the ignitor element and the ohmeter is reading an open connection. I would think a good one would read 20 or 50 or 100 ohms? Some value of resistance other than infinite? The connector has 2 blue wires to the ignitor and one copper (clear insulation) going to the sensor on the same assembly, it inserts vertically on the top-right of the SV9500. I pulled the ignitor element and it still tests open, and I can see a small line going across one side of the element up near the tip, not sure if it's a crack, could be?

    Advice?
    Spiff59's Avatar
    Spiff59 Posts: 5, Reputation: 1
    New Member
     
    #5

    Jan 31, 2009, 12:16 PM
    How smart is a Honeywell SV9500 smart valve?

    The heating element on my flame rod assembly is cracked, it doesn't glow and it tests as an open connection.
    So, to bring the temperature around here above 50 degrees, I thought I'd manually light the pilot, and get one free heating cycle to bring things up to a more comfortable temperature around here. Then, Monday morning I'll chasee down a Q3400 flame rod/sensor assembly.

    I expected to have gas flow at the pilot within the first fes seconds of the furnace starting, which I'd manualy light and throw the cover on before the sensor opened up the main gas flow. I'm not seeming to have any gas flow at the pilot. Is the SV9500 smart enough to detect a cracked (or what it might conside a missing) flame rod and not engage gas flow to the pilot?

    I'm somewhat suspicious that I'd happen to have a dual-failure at the same tme (both flame rod and smart valve)
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Jan 31, 2009, 01:34 PM
    Smart valves have had many problems. The nick name is Dumb Valve in the trade. If you have one of these they are junk also.
    Attached Images
      
    Spiff59's Avatar
    Spiff59 Posts: 5, Reputation: 1
    New Member
     
    #7

    Jan 31, 2009, 01:53 PM

    Yes, that's my ignition system, and the HSI is cracked. I'm guessing the SV9500 detects that the HSI wires are showing an open connection, and therefore won't provide gas to the pilot. So, I guess I won't fooling the furnace into providing some heat prior to Monday. I'll take your word that the SV9500/Q3400 setup isn't the sweetest, but I just want to fix what we have, not replace the entire furnace. I'll stick in a silicon nitride replacement Monday and expect that'll patch me up for a while.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Jan 31, 2009, 03:32 PM
    I hope it works out for you.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Age of Tempstar SP80 [ 1 Answers ]

I own a condo that I am selling. Showed it tonight and the potential buyers asked how old the unit was. It is a Tempstar SP80 but I have crawled all around the unit looking for a plate with a serial or date. Cannot find one. Does anybody know the date range that this model was made so I can at...

Heil SP80 Won't Ignite [ 11 Answers ]

Last night when I went to bed the furnace was working fine. The power flickered on and off all night, and at 5 am I woke up freezing my butt off. It was 52 degrees in my house. I can hear it the furnace running, but it is not blowing any heat through the vents in my house, nor is it taking in...

Heil sp80 gas settings [ 4 Answers ]

Good Day: Our furnace is a Heil SP80 model #NU65100BFB2, 100K BTU output, converted to LP gas. The main gas valve failed (Honeywell SV9500M 2682, converted, dead solenoid) We have just put in a new main gas valve (Honeywell SV9501 M2056), and personally put in the gas conversion from NG to...

Heil sp80 gas settings [ 1 Answers ]

Good Day: Our furnace is a Heil SP80 model #NU65100BFB2, 100K BTU output, converted to LP gas. The main gas valve failed (Honeywell SV9500M 2682, converted, dead solenoid) We have just put in a new main gas valve (Honeywell SV9501 M2056), and personally put in the gas conversion from NG to...

Tempstar electronic pilot won't stay lit! [ 9 Answers ]

I have a tempstar sp80 furnace. Last heating season I started having problems with the pilot not working. If I wiggle the ignition harness the pilot would light and stay on until the temperature matched the thermostat then would not turn back on when the temp dropped. Now when I wiggle the harness...


View more questions Search