    Greetings,

    I have an old electric furnace located in my attic. I cannot determine the mfg/model, but estimate the unit to be ~20+ years old. We have owned the house for 2 1/2 years and have had heater problems each season. In the last two years we have replaced burned out heating elements and the heating sequencers. This year we called a service company and they diagnosed a burnt out element and a bad sequencer. The element was replaced, but I decided to do my own diagnostics on the sequencer before paying (again) for another one. I'm not an HVAC guy but very handy with a voltage meter and home improvement/repairs. Here's what I've found and it doesn't seem correct to me. Can someone provide an opinion on the findings.

    Electric furnace info:
    Location - Attic
    Mfg / model - Unknown
    Age - Estimated 20 - 25+ years
    Heating type - Electric
    Heating element wattage - 5Kw
    Number of elements - 3
    Sequencer - "Quad"
    Number of sequencers - 1

    Sequencer diagnostics and wiring info:
    Sequencer - two 2-stack units mounted on a base plate. On the base plate is this information:
    15SH22 309576
    H1-110 C1-110

    Sequencer #1 information (from top of sequencer):
    T-O-D
    12SH22 H24v
    308771 A0546

    Sequencer #2 information (from top of sequencer):
    T-O-D
    12SH22 H24v
    308734 A0548

    Sequencer 1 = M1 & M2, M3 & M4, 24V + / -
    Sequencer 2 = M5 & M6, M7 & M8, 24V + / - (the 24v terminals are jumped across pos -> pos, negative -> negative between sequencers)


    Diagnostics results with the unit cycling on / off:
    With the unit powered off (not calling for heat) M1 / M2 and M3 / M4 carry 240v. When the unit powers on these go to 0v and do not carry voltage until the unit cycles off again.
    With the unit powered on (calling for heat) M5 / M6 carry 0v and ~90s later carry 240v. M7 / M8 carry 120v then go to 0v ~90s later, then a little longer go back to 120v.

    Question: Is it normal to have sequencers "normally closed" as with M1 / M2 & M3 / M4? Also, is it normal to have a mix of 240v & 120v running across a sequencer stack?


    Here's the wiring. The colors are as best as I can determine. Most wires are faded and hard to distinguish the original color:
    Note: High temp thermos & heating elements are designated 1 - 3 for information only. I'm presuming they are wired correctly.

    There are two (double) breakers at the unit. Breaker 1 = 40amp, breaker 2 = 30amp.
    Breaker 1 - Hot (black) -> M1
    Breaker 1 - Hot (black) -> M5
    Breaker 1 - Hot (black) -> Wiring harness
    Breaker 1 - Common (white) -> Wiring harness
    Breaker 1 - Common (orange) -> High temp thermo #1
    Breaker 1 - Common (orange) -> High temp thermo #2

    Breaker 2 - Hot (black) -> M7
    Breaker 2 - Common (orange) -> High temp thermo #3

    M2 -> (purple) Heating element #1
    M3 -> (blue, maybe violet) Wiring harness
    M4 -> (brown, maybe violet) Wiring harness
    M6 -> (purple) Heating element #2
    M8 -> (purple) Heating element #3

    High temp thermo #1 -> (red) Heating element #1
    High temp thermo #2 -> (red) Heating element #2
    High temp thermo #3 -> (red) Wiring Harness

    Sequencer 1 - (yellow) 24v+ -> Wiring harness
    Sequencer 1 - (violet, maybe gray) 24v+ -> Wiring harness
    Sequencer 2 - (purple) 24v- -> Wiring harness
    Sequencer 2 - (purple) 24v- - > Pigtail from 24v-

    Question: Is it possible that the 24v wires are simply reversed, in turn causing the normally closed condition on sequencer #1?

    Thanks in advance for any comments and feedback.

    Sincerely,
    Greg Dotts
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Oct 27, 2008, 10:57 AM
    GregDotts's Avatar
    GregDotts Posts: 9, Reputation: 1
    New Member
     
    #3

    Oct 27, 2008, 11:17 AM
    Hello HVAC1000.
    I'm not an electrician but have reviewed the documents that you suggested.
    My main question is, is it normal for this sequencer (White/Rodgers 24A34-6) to have "closed" switches when the thermostat is open (off)? If not, does this indicate a bad sequencer or improper wiring?

    Thanks for the help.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Oct 27, 2008, 11:57 AM
    This diagram might help you to better understand sequencers.

    Part number Q106 is the same as 24A34-6

    http://www.supco.com/images/pdfs/Man...s%205-1-07.pdf

    Sequencers are designed as a time on time off device.

    Problems happen with electric heaters when

    The connections are not tight on all the electrical components and the wire terminal allows the wire itself to deteriorate a inch or so under the wire jacket. (You cut off the old terminal and attach new but the wire is still bad in the new attachment area.) THIS IS A COMMON PROBLEM SEEN ON PREVIOUS REPAIRS.

    The age factor (parts are only designed to last so long)

    The wire heating element sag factor and breakage. This is also a problem of age but also a stress factor from not enough air movement to help keep them cooler over time. (less air over coils allow them to heat up more and in turn this stresses the element more over time)
    GregDotts's Avatar
    GregDotts Posts: 9, Reputation: 1
    New Member
     
    #5

    Oct 27, 2008, 12:55 PM
    Quote Originally Posted by hvac1000 View Post
    This diagram might help you to better understand sequencers.

    part number Q106 is the same as 24A34-6

    http://www.supco.com/images/pdfs/Man...s%205-1-07.pdf
    Thanks hvac1000, this helps a great deal. I've been in the attic again with some new info.

    With the thermostat off (not calling for heat)...
    M1/M2, M3/M4, M5/M6 are closed circuit drawing 240v across the switches.
    M7/M8 is closed circuit drawing 120v across the switch.

    With the thermostat on (calling for heat)...
    M1/M2, M3/M4 are open circuit drawing 0v across the switches.
    M3/M4 is open circuit drawing 0v then ~90s later it closes drawing 240v.
    M7/M8 is open circuit drawing 0v then closes drawing 120v, then opens drawing 0v.

    This all seems completely backward from Q106 in the document you suggested. I have checked the wiring against the schematic on the unit and it all seems wired correctly to me, but I can't really read schematics. I just follow the lines around. So the only conclusion that I can come up with is that the sequencer must be bad. It's a $30 part so I'm just going to replace it and see what happens. Hopefully the darn thing will start working again.

    Thanks for your help.

    I'll post my results after the sequencer change for future users benefit.

    Also, sorry for the original double post. I tried to edit my original post and it updated as a new post.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Oct 27, 2008, 01:03 PM
    As per the diagram those units are supposed to be open and close on a timming basis to activate the heat. Post back with results.
    GregDotts's Avatar
    GregDotts Posts: 9, Reputation: 1
    New Member
     
    #7

    Oct 28, 2008, 08:15 AM
    Follow-up post

    After all my diagnostics and troubleshooting I'm not sure I ever isolated the problem. However, the replacement part was cheap ($20.00) and took about 15 minutes to switch out. The new part fixed the problem and the heating unit is now producing warm air as it should.

    The best I can conclude is that one of the stages of the 4-stack sequencer was bad.

    Thanks for your assistance HVAC1000!
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Oct 28, 2008, 10:35 AM
    Sequencers can be difficult to trouble shoot if you are at the job but almost impossible over a message board. Glad you got it going.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Day & Night electric furnace not heating well [ 1 Answers ]

My Day & Night 517E electric furnace runs a long time and does not heat as well as it used to. This is relatively recent. The air from the registers _seems_ cooler and the furnace does not reach it set point most of the time. During the day, it will sometimes get to the set point, but at night,...

Furnace not heating the house. Damper on the furnace not opening. Motor then shuts. [ 4 Answers ]

My forced-air furnace is not working correctly. The gas works heating the air in the furnace, but When the motor starts the damper doesn't open and the Motor shut down. I need suggestions?:mad:

Cost of converting electric heating to gas heating [ 2 Answers ]

I am buying a house with electric heat. I have heard it can be a lot more expensive than gas. What would be the cost of converting the house to gas heating and a/c?

Electric Furnace - heating element [ 3 Answers ]

I am trying to convert from my broken boiler furnace to an electric furnace. I have central air and all the vents from that. Can I just buy a heating element and put it into the air handler? If I can, how do I know what size heating element to buy? The search on the internet gave 10 and 15 KW...

Electric heating to gas heating conversion [ 1 Answers ]

Hi All, I am new to the site and wanted to know if anyone could assist me with a general quote for electric heating to gas heating conversion on one floor of a three story apartment building. Here are the specifics: 1000 square foot area; 8 rooms; 6 electric baseboards. Thanks.


View more questions Search