    Basement Finishing Electrical
    We are finishing a 1600SF basement... 200A Service Panel with 12 open slots...

    I want to run 14-2 and 14-3 for the entire project... 15A circuits with no more than 8 outlets or 6 recessed lights with 65W floods on any one breaker...

    Also have a bathroom with a shower going in...

    In the bathroom can I run one 15A circuit for 4 lights, one GFCI and the exhaust fan?. The lights and fan WILL NOT be GFI Protected... I'm wondering if the exhaust fan needs to be on its own circuit??

    Also... Is it code to have any outlets controlled by wall switches in a basement??
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Apr 5, 2008, 05:59 AM
    A bathroom is required to have at least one 20 amp circuit for the receptacle. You may have the lights and fan just for this bathroom on this circuit, with GFI protection only needed for the outlet.

    The fan will not need a separate circuit, unless it is the type that has a heater built in.

    All the lights and outlets in the other rooms outside of the bathroom will need Arc Fault protection. This is best done with 2 wire cable to each circuit and outlet, no shared neutrals.

    Each room is to have a lighting outlet with at least one switch, this can be ceiling lights, or at least one switched wall receptacle for table lamps.

    You will also need at least one smoke detector in the basement, and one in each room that will be a bedroom. You will need to check local code to learn if smoke detectors need to be Arc Fault protection for these.

    You may use #14 for the basement wiring, other than the bathroom, which needs all #12. You may be better served by using 20 amp circuits and all #12 wire for the entire basement, but not necessary.

    Any general purpose outlets left in any unfinished area of the basement still needs GFI protection. Not so for outlets for sump pumps, refrigerators, etc.

    This is all based on the 2008 National Electric Code. You should consult with local codes for any changes, and apply for permits.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Apr 5, 2008, 06:03 AM
    OK, you can run #14 for everything except the bath receptacle. That MUST be on a 20A circuit. If the circuit does not leave the bath you can put everything in there on that one 20A circuit. Or you can just have the receptacle and share the lighting and fan with another circuit.

    NO, the fan does not have to be dedicated. It is a tiny load, equal to about one light bulb.
    The only time you need GFI protection for the fan is if it is over the tub/shower.

    Also, you can have WAY more than six recessed cans on a 15A circuit. Like 15-20 if you need. With multiple switches the load is VERY diverse.

    Certainly you can have switched receptacles in a basement. Nothing wrong with it.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Apr 5, 2008, 06:07 AM
    TK brings up a good point.
    Be VERY careful with basement bedrooms. Building codes are VERY strict with regard to this. Things like window area and means of egress. Those tiny basement windows DO NOT cut it for a bedroom.
    In many cases it is not worth it to even have bedrooms.

    And I agree to check with your local code office. See what electrical codes you are under. Arc faults may not be required at all, or only for bedroom receptacles. It depends on your code cycle and if there are any amendments.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Finishing basement [ 2 Answers ]

I just wanted some advice and opinions on basement insulation. I finished part of the basement a couple of years ago, and want to finish the rest. The original part I finished with 2x4 studs, 16 inch centers, and R-12 pink fiber insulation. I'm going to do the rest with 2x4 24 inch centers this...

Finishing Basement [ 2 Answers ]

There are multiple questions that I would like answers to about finishing my basement. First question is drop ceiling. I am OK with installation and understanding the grid pattern. I want know what recessed lights can be used, how many are needed per sq. footage and bracing requirements for...

Finishing Basement Electrical [ 3 Answers ]

Hello. Great site! I have been working on a plan to finish my basement and I would like to run the electrical plans by you and ask some questions. This will be a little long, sorry. First a little background. I am Electrical Engineer, but deal mostly with small electronics. I am going to submit...

Finishing a Basement [ 5 Answers ]

Approximately how much will it cost to finish a basement on our own, with an added 1/2 bathroom, laundry room (not counting the appliances), a small wine celler, and a living area? I realize that a lot will depend on the quality of products that we use, but I was just wondering an average range. ...

Basement Finishing [ 1 Answers ]

I'm starting to finish a basement that is 15' high. Where the bathroom is at will only be framed 8' with a sheetrock ceiling and a plywood floor above that for storage. My question is will the walls of this bathroom be considered load bearing? And can I get away with 2x6 joists spaced 16" above?...


View more questions Search