Ask Experts Questions for FREE Help !
Ask
    loupi01's Avatar
    loupi01 Posts: 92, Reputation: 1
    Junior Member
     
    #1

    Mar 31, 2008, 10:20 PM
    Electrical for shed
    I am building a 12'x12' shed and want to run some electricity. I will have 2 20 amp circuits and 1 15 amp circuit for the lighting. I will run wire from the main panel on side of house to new sub panel in shed. Distance to shed is about 120 feet from main panel. What size sub panel would you install 40, 50 or 60 amp panel and what gauge wire would you use for the amperage suggested.

    I have not heard from tkrussell in a while.

    thanks
    Credendovidis's Avatar
    Credendovidis Posts: 1,593, Reputation: 66
    -
     
    #2

    Mar 31, 2008, 10:30 PM
    Quote Originally Posted by loupi01
    What size sub panel would you install 40, 50 or 60 amp panel and what guage wire would you use for the amperage suggested.
    First of all : all domestic power wiring exceeding 90' at 50 amps or higher requires 4/0 wire. To save money you can use aluminum conductors.

    References :

    List 1 : wire-gauges

    List 2 : amps-wire gauge

    With 2 20 amps circuits and 1 15 amps circuit your feeding breaker should be 60 Amps.
    You can use 3 x 4/0 cable (25 mm = 1" diameter).
    Install underground in conduit.
    Success!
    ;)
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Apr 1, 2008, 04:10 AM
    Loupi,

    Please ignore post #2. This is based on 12v circuits and is completely irrelevant to what you are doing at 120/240v.
    The notion of 4/0 wire for a 50a-120/240v feeder at 90' is ludicrous.



    For a 50A sub-panel run #6cu in conduit out to the shed. 120' is not that far and the voltage drop is WELL within spec even at the full 50A/240v.
    The small amount of 120v circuits you will have will be of absolutely NO consequence, even if partially imbalanced.
    loupi01's Avatar
    loupi01 Posts: 92, Reputation: 1
    Junior Member
     
    #4

    Apr 1, 2008, 08:16 AM
    Thanks stanfortyman,
    I understood the information from Credendovidis was not for my application when I read it. Do you think I would be able to up the sub panel to a 60A using #6cu wire with the 120' distance? Also what # ground should I run?

    Thanks
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Apr 1, 2008, 10:35 AM
    The thing about voltage drop is it is ONLY a concern with regard to the load. You can run #6 to a sub-panel in conduit the whole way on a 70A breaker. 120' is not that far.
    IF you were to draw over 60 or so amps there will be more than a 3% drop in voltage. This is more then the recommended amount of drop, but it is still within reason and will not do any harm.

    If you use a 60A breaker you will be FINE, even at a full 60 amp load on the panel.

    Thing is, if you will use any NM cable as part of this circuit you cannot use a 60A breaker, you would need to drop down to a 50A. THHN conductors in conduit are rated higher than NM cable for this size wire.
    loupi01's Avatar
    loupi01 Posts: 92, Reputation: 1
    Junior Member
     
    #6

    Apr 1, 2008, 11:06 AM
    Thanks stanfortyman,
    You have been very helpful
    mr500's Avatar
    mr500 Posts: 181, Reputation: 8
    Junior Member
     
    #7

    Apr 2, 2008, 05:12 PM
    Quote Originally Posted by Credendovidis
    First of all : all domestic power wiring exceeding 90' at 50 amps or higher requires 4/0 wire. To save money you can use aluminum conductors.

    References :

    List 1 : wire-gauges

    List 2 : amps-wire gauge

    With 2 20 amps circuits and 1 15 amps circuit your feeding breaker should be 60 Amps.
    You can use 3 x 4/0 cable (25 mm = 1" diameter).
    Install underground in conduit.
    Success!
    ;)

    UMMMM What!!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Power to my shed [ 1 Answers ]

I want to run permanent power to my shed. I am trying to power a very small wood shop. This includes, circular saw, single stage air compressor, radio, 2 4' fluorescent light balasts, and a small router from time to time , small box fan. The run is 50' from the house and another 30' to the panel...

How to Rehab a Shed? [ 6 Answers ]

I have a 11 ft by 28 ft shed I am looking to rehab and live in as a one room efficiency. Problem is, it needs a lot of work. I'm a woman so I really don't know much about these kind of things, and would greatly appreciate any help or suggestions. It has large cracks in the walls that need to be...

Power To A Shed [ 15 Answers ]

My 14 by 32 shed will be ready to go in a couple of weeks and I am trying to figure out what size wire I need to run from the panel on my house to the shed. It will have 6 110 outlets,1 220 outlet and 2 light outlets. I will primarily be running power tools and a air compressor that is 110. The 220...

Wooden shed [ 2 Answers ]

I have a large wooden shed by my house we just had a tree cut down I would like to move it to the back of the yard what's the best way to move one of these sheds

Wiring a shed [ 2 Answers ]

I just finished building a storage shed and want some electricity out there... what type of wiring and cost would it be to run 30-40 feet or wire?what other materials am I going to need? Thanks for any suggestions... later


View more questions Search