Ask Experts Questions for FREE Help !
Ask
    tableclocks's Avatar
    tableclocks Posts: 432, Reputation: 2
    Full Member
     
    #1

    Mar 27, 2008, 07:42 PM
    20 kw furnace
    Follow up on my furnace... it has 2 240 60 amp brakers built in... do I have to use 2 240 60 amp brakers in my 200 amp service panel? 6/3 wg wire? That's 2 lines of 6/3 wg from my panel to my furnace?. thank you
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #2

    Mar 27, 2008, 07:59 PM
    Your system should have a rating plate telling you what you need. With 20 kw the heat strips will be around 84 amps the blower may pull around 5 or 6 amps.
    Credendovidis's Avatar
    Credendovidis Posts: 1,593, Reputation: 66
    -
     
    #3

    Mar 27, 2008, 08:02 PM
    Yes # 6 copper is the proper size for a 60 amp breaker.
    You mention 2 pcs 240 Volts 60 amps breakers.
    That means two circuits each of 60 Amps at the furnace.
    Which requires 2 sets of wires rated for 60 Amps (=6 copper) from the furnace breakers to the service panel. And on the panel 2 breakers of first available higher rating than 60 Amps.
    Don't forget the earth wires.
    Success.
    :)
    erjskashyap's Avatar
    erjskashyap Posts: 2, Reputation: 1
    New Member
     
    #4

    Mar 28, 2008, 03:06 AM
    Pl. Tell me 0totel summary of close & open loop in HVAC.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search


Check out some similar questions!

Wiring a furnace thermostat to manually operate the furnace fan [ 2 Answers ]

I have two wires connected to my furnace thermostat. There is a place labeled G on the thermostat. Can I simply run a wire from the G terminal on my thermostat to the terminal labeled G on my furnace fan relay to operate the fan separately?

York Stellar Furnace Heating up Furnace Room to 110 Degress? [ 2 Answers ]

I have a York Stellar Furnace in my newly purchased house. Furnace is 15 years old. Furnace is releasing hot air from front grills and heats up furnace room to 110 Degrees. I had a Bryant Furnace in another house and this never happened. All plenams and ducts are taped and sealed so the heat is...

Goodman furnace GMNT080-4 furnace runs good for a while then has to be manually reset [ 5 Answers ]

I have a Goodman GMNT080-4 (90%). I'm having the same problem As Streatherg did back in the Nov 2006 question. I reviewed his article and tried Every thing on there but seems to be doing the same thing. The furnace kicks on for about an hour then locks out and has to be manually reset threw...

Furnace not heating the house. Damper on the furnace not opening. Motor then shuts. [ 4 Answers ]

My forced-air furnace is not working correctly. The gas works heating the air in the furnace, but When the motor starts the damper doesn't open and the Motor shut down. I need suggestions?:mad:

Comfortmaker Furnace Fan blows in line fuse and will not allow furnace to work [ 1 Answers ]

I have a Comfortmaker Furnace (approximately 1998/99) and the fan will not turn on allow the furnace to heat. When I try to turn the furnace on it blows a 3 amp fuse at the blower motor. I removed the fuse and jumped it and all it will do is make a faint buzzing noise and not turn on. I can...


View more questions Search