  • Mar 27, 2008, 07:42 PM
    tableclocks
    20 kw furnace
    Follow up on my furnace... it has 2 240 60 amp brakers built in... do I have to use 2 240 60 amp brakers in my 200 amp service panel? 6/3 wg wire? That's 2 lines of 6/3 wg from my panel to my furnace?. thank you
  • Mar 27, 2008, 07:59 PM
    T-Top
    Your system should have a rating plate telling you what you need. With 20 kw the heat strips will be around 84 amps the blower may pull around 5 or 6 amps.
  • Mar 27, 2008, 08:02 PM
    Credendovidis
    Yes # 6 copper is the proper size for a 60 amp breaker.
    You mention 2 pcs 240 Volts 60 amps breakers.
    That means two circuits each of 60 Amps at the furnace.
    Which requires 2 sets of wires rated for 60 Amps (=6 copper) from the furnace breakers to the service panel. And on the panel 2 breakers of first available higher rating than 60 Amps.
    Don't forget the earth wires.
    Success.
    :)