    Main circuit breaker
    The main circuit breaker keeps triping when it gets hot could it be old and need changing
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Mar 8, 2008, 03:53 PM
    It could be lots of things. However, because this is the man breaker and to repair it requires that the meter be pulled, I would call an electrician now.

    Pulling the meter is an extremely dangerous task, if you don't know exactly what you are doing.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Mar 8, 2008, 04:30 PM
    Pulling the meter IS illegal in most areas.

    Call an electrician to check this out.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Mar 8, 2008, 04:43 PM
    Pulling the meter IS illegal in most areas.

    I totally agree.

    Also drop the load if you do or the meter contacts could flash in your face.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #5

    Mar 9, 2008, 09:19 AM
    Pulling a Breaker is OK to be pulled by someone who can safely work with Eletrical.
    The Breaker Can get Hot if the Wires are loose on breaker, Bad connections the breaker plugs onto. If you had an Amprobe and clamped around, wires, you could see maybe Bad Breaker(Example 40 amp draw on 200 Amp breaker making it very warm would be bad internal connections).
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #6

    Mar 9, 2008, 09:53 AM
    Strat,

    I have to give it to you, you are pretty good when it comes to troubleshooting!
    I agree on the loose connection at the main. For the most part, everyone has contributed good information!
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #7

    Mar 9, 2008, 01:20 PM
    Strat,

    Did I miss something , again? The poster is telling us that his SEP breaker is tripping, correct. The only way I know of to change the main breaker is to kill the power from the meter into the SEP main breaker. As I also understand it this should never be done by a novice!
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #8

    Mar 9, 2008, 02:46 PM
    If the Panel is Main Lug, Simply change breaker like usual, If panel had no spot for main, then that breaker may be "Backfed, and should be bolted, If Main Breaker Panel, then It should be easy to change like regular breaker.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #9

    Mar 9, 2008, 03:02 PM
    Quote Originally Posted by Stratmando
    .......If Main Breaker Panel, then It should be easy to change like regular breaker.
    This is completely NOT so!!
    A main breaker has the service entrance conductors, the UNFUSED and LIVE service entrance conductors, connected to the breaker.

    THERE IS NO SAFE WAY to do this live!!!!!!!! Especially for a novice.

    Besides, the OP states this is the main breaker. One can only assume it is a typical main breaker panel.

    I do agree that it is likely corrosion on the main buss stabs where the breaker connects. This is a common issue.
    CALL AN ELECTRICIAN to have this looked at.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #10

    Mar 9, 2008, 03:14 PM
    Stanforty, I tried to give you Agree, But said I must spread Some more stuff around, You are correct, Was thinking more Disconnect, I work with Live so much, I am Cautious, Stay Isolated from ground, and connect with no load.
    It has been a long time since changing a breaker has scared me.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #11

    Mar 9, 2008, 03:30 PM
    I had a feeling it was probably a mistake you posting that. We all know we can change a breaker like that because we know how it is done and the precautions to take.
    A DIYer is a bit different.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #12

    Mar 9, 2008, 03:53 PM
    I've changed breakers on a hot panel from time to time just so that I don't disrupt the house.
    But unless there is an outside Service Disconnect panel box, not a chance in the standard time zone will I handle the R&R of the main panel breakers.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #13

    Mar 9, 2008, 04:53 PM
    As was stated above,

    It can be loose conductors.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Theory of vacuum Circuit Breaker & sf6 circuit breaker [ 15 Answers ]

I want to know about the basic Theory of vacuum Circuit Breaker & sf6 circuit breaker

Difference between Main Lug and Main Breaker Panel [ 8 Answers ]

What is the difference between a Main Breaker Panel and a Main Lug Panel and can either be used in new residential construction.

Load Center Main Lug or Main Breaker for the Attic [ 5 Answers ]

I have a large attic (on 3rd floor), 38'x28', which is unfinished space. The 2nd floor central air-condition is located there and used to be fed by a 60 feet of 12/3 cable (I changed the cable to 10/3 to reduce the chance of voltage drop) and it's fed by a dual 15A breaker (240v breaker) in the...

Can I convert a main breaker Cutler Hammer loadcenter to main lug? [ 1 Answers ]

I was wondering if Cutler Hammer made a part to convert a main breaker load center (CH) style, to a main lug panel. If so, does anyone know the part number or can you refer me to a location where I could find it? Cutler Hammer's website is not too user friendly. Thanks

Blowing Main Circuit Breaker [ 1 Answers ]

I have a electric dryer that is 220 volt. When I turn it on, after about 15 minutes it doesn't blow it's own 30 amp breaker, but blows the 100 amp main breaker. I can shut off the 30 amp breaker specifically for the dryer and it shuts it off. Any ideas??


View more questions Search