    Adjusting gas boiler flame
    I have a Vulcan floor standing gas boiler, some 30 years old. Recently I have had problem with the pilot light going out, maybe once a week. It seems worse when we have windy weather, but when I watch the main burner igniting/extinguishing (using the thermostat knob), the pilot light seems to 'stagger', as if the gas pressure to it is being affected by demand from the burner.
    The gas valve is Honeywell, and I have adjusted the pilot light to give a good strong blue flame. The main burner is also adjustable, but I do not know the correct adjustment - the burner flame seems OK for the first 5 to 10 seconds, but then builds up in intensity and appears too fierce.
    Any advice will be gratefully received. Thanks.
    biggsie's Avatar
    biggsie Posts: 1,267, Reputation: 125
    Ultra Member
     
    #2

    Feb 23, 2008, 09:44 PM
    I think you have your answer " It seems worse when we have windy weather"

    This is caused by a downdraft (wind) that blows out the boiler pilot light

    Does it seem like there is a draft when you try to adjust the flame

    Extending the chimney can help -- hope this helps you
    agric's Avatar
    agric Posts: 2, Reputation: 1
    New Member
     
    #3

    Feb 24, 2008, 07:19 AM
    Thanks for your reply, biggsie. However, I failed to mention that the boiler has a balanced flue, direct to the external wall, and about 15 feet above ground. This whole installation has worked OK for some 30 years - only recently has the problem occurred. I checked the flue yesterday, and only fault I could see was poor mortar seal between the metal flange of the flue and the wall, which I rectified. BUT, when I removed the blanking plate on the boiler front to inspect the flue from inside the house, I was surprised at the strength of the incoming draught of air, as the flue appears to be designed to prevent that.
    G Vinnie's Avatar
    G Vinnie Posts: 1, Reputation: 1
    New Member
     
    #4

    Mar 16, 2008, 08:34 AM
    I am having the same problem with an old Vulcan Continental boiler. The downdraft has got so strong that I can't even light the pilot light. How can I fix this?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Mar 16, 2008, 09:03 AM
    The main gas valve has to be adjusted to the rate plate on the unit. There will be a firing rate /water collum figure that it has to be set to and it will read in inches of water.You need special tools to do this and I highly recommend a professional make the adjustment. You can tell nothing by just eye balling the flame.

    One more item. On those boilers sometimes a draft diverter type piece of metal will rust away causing a down draft situation.
    biggsie's Avatar
    biggsie Posts: 1,267, Reputation: 125
    Ultra Member
     
    #6

    Mar 16, 2008, 09:54 AM
    What I think is deflect draft at boiler or deflect it at the vent

    So wind goes past it or is deflected over the top of it

    Maybe it just needs a different cap -- different shape
    boilerman44's Avatar
    boilerman44 Posts: 1, Reputation: 1
    New Member
     
    #7

    Dec 6, 2011, 12:36 PM
    We had same prob, just had to keep relighting boiler I'm afraid.
    Does any body know where I can get a thermostat from for the same boiler Ta.
    Kevthegas's Avatar
    Kevthegas Posts: 1, Reputation: 1
    New Member
     
    #8

    Jan 12, 2012, 12:02 PM
    I balanced flue is call that because the incoming air and outgoing products are in the same air pressure zone so the wind pressure is balanced, the problem will be a damaged rope seal causing the boiler to become unbalanced. A gas safe registered engineer will easily solve this problem for you

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Gas furnace - no flame [ 4 Answers ]

Hope someone out there can help, because it's going to get cold this weekend! I have a split HVAC unit with furnace in attic. Written on front of unit is Intertherm. Inside panel of unit says Nordyne, and the Ignition Control is Robert Shaw. The unit is 13 years old and the heat worked fine...

Flame on Vailiant Boiler (propane) [ 1 Answers ]

The flame (propane) on our 10 yr old Valiant boiler I(Has 3 zones) is sometimes burning yellow not blue. There are two burners. Each burner has a long grated area inside through which the fuel is burned. The flame looks correct most of the time but occasionally The blue flame occurs in the tube...

Gas Fireplace Will Not Hold Flame [ 1 Answers ]

We moved into a used (10 years old) house with a Heatalator gas fireplace.  It was supposed to be working, but we could not get it to hold a fire.  The fellow who passed it before closing said it held for him.  But he could not get it to work for us.  He spent 5 hours changing over everything...

Gas dryer trouble with flame [ 1 Answers ]

My Kenmore gas dryer takes 2 or 3 cycles to do what it used to in 1 cycle. Observing the flame, it runs about 45 seconds then cuts off even with a full wet load. It will cycle back on then shut off again after running about 45 seconds. I suspect that either the thermal limiter, wherever that is, is...


View more questions Search