    Heatpump not working
    I have a lennox heat pump and when it is turned on in the heat mode the head pressure goes up 500psi and compressor starts to over amp but when it is turned over to coolling the unit runs fine it is a 410a unit
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #2

    Feb 9, 2008, 07:47 PM
    You have a bad txv or a restriction at the piston on the out door unit.
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #3

    Feb 9, 2008, 07:52 PM
    Is your indoor fan running during this time in the heat mode? And is the filter clean, possibility of low or no air movement?
    John Crossing's Avatar
    John Crossing Posts: 2, Reputation: 1
    New Member
     
    #4

    Jul 10, 2008, 06:26 PM
    Thermostats can change the pressures if they are bad on heatpumps might be the thermostat.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Jul 10, 2008, 09:01 PM
    Thermostats can change the pressures if they are bad on heatpumps might be the thermostat


    Makes no common sense.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heatpump not working - not putting out heat [ 1 Answers ]

Last summer we had a leak in the ac - we gased up and it worked fine. Now that it is cold, i keep my heater on 64* , this morning my heater was not working and not warming the house. I raised the thermostat to 70* and still no action. Went outside - frost around the unit and fan not...

Outside condenser (heatpump) not working in cooling mode [ 2 Answers ]

My Goodman heatpump consonsor will not start in cooling mode. I have 240 volt and 24 volt at the condenser, but the unit still won't turn on when I call for cooling. The unit has a defrost circuit board. Need help. Thanks

Installing heatpump or AC [ 5 Answers ]

Hi I'm remodeling a house built in '32, with an addition in the 40s or 50s. The house is about 1200sq ft (800 sq ft w 9' ceilings, 400 sq ft with 8'ft ceilings) with a 1/2 basement where the heater (oil) water heater, circuit panel etc. At present there is no AC in this house, although the air...

Heatpump thermostat [ 1 Answers ]

I have a goodman heatpump with a janitrol 1890 thermostat it has never switched the aux heat on .When the temp gets too cold for heat pump to make heat .I have to turn emergency heat on myself .Book says model1860 thermostat is what should be installed is this my problem if so a new thermostat...

Runaway heatpump [ 5 Answers ]

I have a 1400sq foot 2 story home built in 2005 with a single heat pump. The thermostat is located on the first floor. During the winter the heat will run and run to try to maintain the temperature on the first floor but the second floor will bake. For example, the first floor may be set to 70 but...


View more questions Search