Gas Valve Shuting off
Have a carrier 58DR075-AA Series 121. Pilot was lighting but main gas to burners was not opening. I replaced pilot/thermocoupler unit, its all one piece. Now the pilot lights after a few seconds I hear the burner valve open, and the burners try to light but go right out. Other times the pilot clicks off before the main valve opens and it keeps retring. Only occationaly does it light and come to temperature but after it retries I face the same problem. Am I missing something? I have checked the voltage on the circuit board and it is sending a voltage to the valve to open.
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 28, 2008, 05:05 AM
|
|
If it is sending a steady 24 volts to the gas valve when the gas valve turns off no reason it would seen to me to be a gas problem valve. All other requirements for unit operation must be met for the unit get the 24 volts to operate the gas valve to start with.
Replacing the gas valve is never my first choice in a repair because they usually last for a very long time and cost some $$$.
If you feel that all other devices on the furnace are working properly then you will have to make the choice as to weather or not you replace the valve.
|
|
 |
Junior Member
|
|
Jan 28, 2008, 06:38 AM
|
|
Another important thing to check is proper gas pressure to the burners as per the ID plate spec. on that unit, as well as incoming gas pressure to the gas valve...
|
|
 |
New Member
|
|
Jan 28, 2008, 06:41 AM
|
|
 Originally Posted by bspata
Have a carrier 58DR075-AA Series 121. Pilot was lighting but main gas to burners was not opening. I replaced pilot/thermocoupler unit, its all one piece. Now the pilot lights after a few seconds I hear the burner valve open, and the burners try to light but go right out. other times the pilot clicks off before the main valve opens and it keeps retring. Only occationaly does it light and come to temperture but after it retries I face the same problem. Am I missing something? I have checked the voltage on the circut board and it is sending a voltage to the valve to open.
hvac1000 Thanks. The valve seems to be working but the 24v from the board to the valve is only on momentarily when it tries to ignigte. When it does lite it is blowing right out immediately and the voltage to the valve ends. It seems that it is tiring to lite less often and the pilot is clicking off before the burner valve opens. Only sometimes does it acually fire up. Then only for one cycle.
|
|
 |
Junior Member
|
|
Jan 28, 2008, 06:48 AM
|
|
How is the pilot height? It needs to be high enough to cover the flame rod and the back metal bracket of the pilot assembly?
|
|
 |
New Member
|
|
Jan 28, 2008, 06:53 AM
|
|
 Originally Posted by tsa7man
Another important thing to check is proper gas pressure to the burners as per the ID plate spec. on that unit, as well as incoming gas pressure to the gas valve...
Thanks tsa7man, The furnace is Nat gas from the street. Comes in on 3/4" feeds two furnaces. one to the house and one to the shop. it is the one to the shop giving the problem. It has a 1/2" line going 50'+- It has always worked to this point. I'm not sure where a press. Drop could be. Is the pressure adjustable at the valve some how?
|
|
 |
New Member
|
|
Jan 28, 2008, 06:58 AM
|
|
 Originally Posted by tsa7man
How is the pilot height ?? It needs to be high enough to cover the flame rod and the back metal bracket of the pilot assembly ??
Thanks again; this seems like it could be a possablity; where as I just replaced the pilot. Thanks. I will check it. I mounted it in the same position as the old but noticed the flame is larger than the old pilot was. About 3/4' to 1"..
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
No gas supply, or faulty valve in gas fireplace?
[ 4 Answers ]
We use a regency Gr55-3 ~20,000btu gas fireplace for heating our bedroom. Its about 10 years old and has given us no trouble before.
The gas supply line is a small (3/8"?) flexible copper tube that runs about 40' from a prv. I believe the prv lets pressure down from 2psi to a few inches of...
Maytag gas dryer, replacing gas valve coils
[ 5 Answers ]
Hi, I hope someone can help me.
My Maytag gas dryer's igniter glows but then no flame appears. I believe it is the gas valve coils that are bad, so I purchased a replacement kit (3 coils). The instructions say to match the colors of the wires, but my replacement kit has red, black, white...
91 honda accord shuting off
[ 1 Answers ]
I have a 91 honda accord that is shutting down while driving. I have replaced the main module, ignition switch, and fuel pump. It nows seems to be when fuel is low. It will usually start right back up. Is there anything else I can check or replace??
Gas valve noise on main valve engagement
[ 1 Answers ]
I have a carrier 58gs100ga furnace with a white rodgers 36e93 gas valve. The main gas valve solenoid chatters or rattles for a split second before it stays engaged after the pilot is proved. I just replace the spark/lock out board and the fan board for a different problem. This chatter is...
View more questions
Search
|