New Member
|
|
Jan 25, 2008, 08:18 AM
|
|
Carrier 58ES125-2D or 5BES125-2Pilot comes on for approx 2-3 sec goes out I replaced
Carrier 58ES125-2D or 5BES125-2Pilot comes on for approximately 2-3 d
Seconds clicks shuts off and retries over and over any ideas, may even click as it goes on?
Thanks
I replaced the flame sensor same thing pilot starts and goes out 2-3 seconds.
What's next the proven pilot control?
Thanks for the help
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 25, 2008, 02:11 PM
|
|
Usually that is a flame sensor problem. The new one is clean and installed properly?
You might try to clean the pilot orifice to make sure the pilot is the correct size so the flame sensor can activate the safety control.
Dirt/spider webs etc can get into the pilot orifice.
Pilot orifice located in pilot housing. Care should be taken since the pilot hole is very small. Usually a VERY small wire run through the hole will do the trick.
|
|
 |
New Member
|
|
Jan 25, 2008, 02:25 PM
|
|
 Originally Posted by richv
Carrier 58ES125-2D or 5BES125-2Pilot comes on for approximately 2-3 d
seconds clicks shuts off and retries over and over any ideas, may even click as it goes on?
Thanks
I replaced the flame sensor same thing pilot starts and goes out 2-3 seconds.
Whats next the proven pilot control?
Thanks for the help
Thanks I will try that tonight1
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 25, 2008, 02:35 PM
|
|
Word of caution. Use some WD-40 or equivalent on the aluminum tube where it goes into the brass break off nut. Aluminum corrodes and if you do not give it some lube it may twist or break. If that happens you will be looking for some new 1/4 inch aluminum tube and two new nuts and that takes all the fun out of it.
|
|
 |
New Member
|
|
Jan 25, 2008, 02:47 PM
|
|
Do I need to take it apart to clean or just move it out for access
Thanks again
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 25, 2008, 05:58 PM
|
|
You need to remove to do pilot so you might as well remove it for both.They are on the same assembly I believe.
|
|
 |
New Member
|
|
Jan 26, 2008, 01:08 PM
|
|
Carrier 58ES125-2D or 5BES125-2Pilot comes on for approx 2-3 sec goes out I replaced
I cleaned pilot orifice the same thing.
Question I removed the lead from the flame sensor to the pilot contol resulted in the pilot not goimg out needless to say furnace did not start, does that mean the pilot control is bad
Thanks
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 26, 2008, 01:29 PM
|
|
Please answer these questions. I do not have a service manual for your model so I am trying to get info from you.
Does your furnace have a GLOW BAR style ignition ? This is also called hot surface ignition. When the thermostat starts the furnace a glowing will come on and then the pilot will light.
Does you furnace have a 3 wire pilot control ? This will be identified by 3 wires going to the pilot area. The unit will spark to lite the pilot then the pilot flame will be established.
Sorry about the additional questions but I am trying to think of all possibilities before you have to buy a expensive circuit board.
|
|
 |
New Member
|
|
Jan 26, 2008, 01:39 PM
|
|
It has two wires going to the pilot the flame sensor and an electrode rod for the spark
So no glow bar,more of what you defined as 3 wire but I only see 2 plus gas line to pilot.Thank you again
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 26, 2008, 05:32 PM
|
|
I normally do not do this but private message me and include your email address. I have a nice checklist for you to follow but it is to big and this site will not allow me to post it here. It is in Adobe format.
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 26, 2008, 06:27 PM
|
|
I just sent you a message on the sticky notes. Did you get it?
|
|
 |
Ultra Member
|
|
Jan 26, 2008, 06:35 PM
|
|
Sounds like you have a bad ignition control. If you have 24v from TH to C on the ignition control box when the pilot is trying to light and after it quits it's a bad ignition control. Common problem with that system.
|
|
 |
New Member
|
|
Jan 26, 2008, 06:46 PM
|
|
What is the TH to C?
Thanks for the help!
|
|
 |
Ultra Member
|
|
Jan 26, 2008, 10:16 PM
|
|
TH is the 24v going into the control after its going through all the limit switches and pressure switch, C is the common side of the transformer. Make sure you have a good ground with the control box, that's what makes the flame sensor work. A short in the gas valve will make it act the same, undo the wire going to mv on the gas valve if the pilot won't stay lit I would say bad ignition control box.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Carrier 58GS125-2, Burner shuts down after 10 Sec, no Blower
[ 6 Answers ]
I am trying to fix a Carrier Model 58GS125-2 with spark ignition.
Thermostat Switches on Heat
Spark Starts
Pilot Lights
After about 10 seconds Burner Starts
After about 10 more second Burner goes out
Pilot stays lit and burner keeps cyling on and off with no blower.
Extra info. 3 Wire...
30 Gallon Water Tank - How Many Showers (approx)
[ 14 Answers ]
I have a 30 gallon gas water tank which is about 7 years old. I rent, pay my own utilities but have to use the plumber the landlord contracts with who is onery, a "know-it-all" and a misogynist! His employees have agreed there is a problem but he overrides them, so I'm stuck between a rock and...
Ammonium Sulfide 3ml (approx) safe outdoors?
[ 1 Answers ]
Hello,
Would 3mL of an Ammonium Sulfide solution be considered unsafe and/or annoying if it were used outside on private property?
I live in a city and want to keep my stoop clear of those wanting to use it as a smoking, foul language and vomit stop (yep, cleaned it up last sat). I have an...
Approx 1980's cartoon dogs with horns (possibly anime/manga)
[ 1 Answers ]
I'm trying to remember a short series/film about this pup that was found by a young boy. The pup belonged to a pack of dogs that resembled alsatians but had horns on their head. The dogs attacked the building where the pup was being held as they were vicious and the horns lit up when...
View more questions
Search
|