-   -   Carrier 58ES125-2D or 5BES125-2Pilot comes on for approx 2-3 sec goes out I replaced (https://www.askmehelpdesk.com/showthread.php?t=176489)

  • Jan 25, 2008, 08:18 AM
    richv
    Carrier 58ES125-2D or 5BES125-2Pilot comes on for approx 2-3 sec goes out I replaced
    Carrier 58ES125-2D or 5BES125-2Pilot comes on for approximately 2-3 d
    Seconds clicks shuts off and retries over and over any ideas, may even click as it goes on?
    Thanks
    I replaced the flame sensor same thing pilot starts and goes out 2-3 seconds.
    What's next the proven pilot control?
    Thanks for the help
  • Jan 25, 2008, 02:11 PM
    hvac1000
    Usually that is a flame sensor problem. The new one is clean and installed properly?

    You might try to clean the pilot orifice to make sure the pilot is the correct size so the flame sensor can activate the safety control.

    Dirt/spider webs etc can get into the pilot orifice.
    Pilot orifice located in pilot housing. Care should be taken since the pilot hole is very small. Usually a VERY small wire run through the hole will do the trick.
  • Jan 25, 2008, 02:25 PM
    richv
    Quote:

    Originally Posted by richv
    Carrier 58ES125-2D or 5BES125-2Pilot comes on for approximately 2-3 d
    seconds clicks shuts off and retries over and over any ideas, may even click as it goes on?
    Thanks
    I replaced the flame sensor same thing pilot starts and goes out 2-3 seconds.
    Whats next the proven pilot control?
    Thanks for the help

    Thanks I will try that tonight1
  • Jan 25, 2008, 02:35 PM
    hvac1000
    Word of caution. Use some WD-40 or equivalent on the aluminum tube where it goes into the brass break off nut. Aluminum corrodes and if you do not give it some lube it may twist or break. If that happens you will be looking for some new 1/4 inch aluminum tube and two new nuts and that takes all the fun out of it.
  • Jan 25, 2008, 02:47 PM
    richv
    Do I need to take it apart to clean or just move it out for access
    Thanks again
  • Jan 25, 2008, 05:58 PM
    hvac1000
    You need to remove to do pilot so you might as well remove it for both.They are on the same assembly I believe.
  • Jan 26, 2008, 01:08 PM
    richv
    Carrier 58ES125-2D or 5BES125-2Pilot comes on for approx 2-3 sec goes out I replaced
    I cleaned pilot orifice the same thing.
    Question I removed the lead from the flame sensor to the pilot contol resulted in the pilot not goimg out needless to say furnace did not start, does that mean the pilot control is bad
    Thanks
  • Jan 26, 2008, 01:29 PM
    hvac1000
    Please answer these questions. I do not have a service manual for your model so I am trying to get info from you.

    Does your furnace have a GLOW BAR style ignition ? This is also called hot surface ignition. When the thermostat starts the furnace a glowing will come on and then the pilot will light.

    Does you furnace have a 3 wire pilot control ? This will be identified by 3 wires going to the pilot area. The unit will spark to lite the pilot then the pilot flame will be established.

    Sorry about the additional questions but I am trying to think of all possibilities before you have to buy a expensive circuit board.
  • Jan 26, 2008, 01:39 PM
    richv
    It has two wires going to the pilot the flame sensor and an electrode rod for the spark
    So no glow bar,more of what you defined as 3 wire but I only see 2 plus gas line to pilot.Thank you again
  • Jan 26, 2008, 05:32 PM
    hvac1000
    I normally do not do this but private message me and include your email address. I have a nice checklist for you to follow but it is to big and this site will not allow me to post it here. It is in Adobe format.
  • Jan 26, 2008, 06:27 PM
    hvac1000
    I just sent you a message on the sticky notes. Did you get it?
  • Jan 26, 2008, 06:35 PM
    T-Top
    Sounds like you have a bad ignition control. If you have 24v from TH to C on the ignition control box when the pilot is trying to light and after it quits it's a bad ignition control. Common problem with that system.
  • Jan 26, 2008, 06:46 PM
    richv
    What is the TH to C?
    Thanks for the help!
  • Jan 26, 2008, 10:16 PM
    T-Top
    TH is the 24v going into the control after its going through all the limit switches and pressure switch, C is the common side of the transformer. Make sure you have a good ground with the control box, that's what makes the flame sensor work. A short in the gas valve will make it act the same, undo the wire going to mv on the gas valve if the pilot won't stay lit I would say bad ignition control box.