    HVAC Wiring or What?
    I have a Goodman GSH130241A Heat Pump, Atrane TWv024140A0 Air Handler, and a White-Rodgers Mfg 1F58-72 thermostat. I've had 2 highly experienced companies out working on our system. The system will heat or cool great if you disconnect the wire going to the reversing valve, depending on if you want heat or cool. They both first said the defrost board was bad. They have each changed it. Still to no correct results. The one replaced wire jacket to out side unit. Right now to have heat I believe he has the reversing valve disconnected. Also they both have said heat strips are not coming on. Could they have something wired wrong or is there a compatabliity problem with the thermostat and units, or is it a simple wiring problem? One of them has also called Goodman for tech for Help. Thank Bearybuzy1
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 23, 2008, 05:38 AM
    Wiring

    http://www.white-rodgers.com/wrdhom/..._06_pg0192.pdf

    Manual

    http://www.white-rodgers.com/wrdhom/.../0037-4046.pdf

    I believe you have a low voltage wiring problem. Above are the manual and a extra wiring diagram. I would go over the entire low voltage system. You should not have to disconnect a wire for it to work. Could be the reversing valve is being fed by the wrong area of the thermostat. Since we are not there you or a company will have to check this out. If you paid the companies to check out your system they should come back to take care of this if you paid them to start with.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Jan 23, 2008, 01:17 PM
    I've seen a similar problem and the seasoned HVAC guy couldn't seem to solve it. Turned out that months after a commercial remodel a Heat Pump developed a similar problem. The t-stat wire got shorted in a metal stud. I was able to troubleshoot it by disconnecting the tstat base and the wires at the HP and checked for shorts. He, erroneously thought it was the stat.

    Running a new t-stat wire fixed it.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jan 23, 2008, 01:31 PM
    I mentioned the wiring but I wanted to add that you can wire the reversing valve two different ways on that thermostat. I used to let sparky run all my power and low voltage. I would let sparky land the power but never the low voltage. To many thermostats ( heat anticipators) up in smoke. LOL
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #5

    Jan 23, 2008, 08:31 PM
    If someone connected the reversing valve wire at the thermostat to the "B" terminal instead of the "O" terminal you would run into this problem. If this unit runs in heat mode with no voltage to the solenoid then it would need to be wired to the "O" at the thermostat. Hope this is helpful, Mike

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

HVAC Wiring Size for Geothermal units [ 6 Answers ]

I've found a number of these type of questions in here and I thought I'd post my own, with what I *think* my solution is. I have two geothermal units The first Geo unit has this... Min CKT Ampacity = 25.6 A Max HACR = 35 A The second unit has this... Min CKT Ampacity = 29.6 A

Simple HVAC wiring issue [ 10 Answers ]

I am switching from Honeywell CT87a (subbase Q539A4034) to Honeywell RTH7400 seems simple enough but I am bad when it comes to this sort of stuff. Anyway. I have Red, White, Green, Blue wiring coming out of the wall and have a electric air/heat system. Currently wired to 7400 as R-R W-Y B-W...

HVAC blower motor--screwed up wiring-- HELP [ 11 Answers ]

Relaced blower motor, but wires are different from old motor--can hear it click on, but nothing else. Have part and model numbers for old motor (GE), new motor (Dayton-PSC), and HVAC (Goodman) Please Help-- am burning up here--(south texas)


View more questions Search