    Dec 23, 2007, 05:38 AM
    Breaker getting hot
    Hello,

    I have a set of common 220 breakers that are tripping, I have tested both wires with a amprobe and both wires are pulling under the limit of the breaker. I'm wondering if a breaker will get hot to the touch if it has gone bad?

    Thanks

    Jim
    MOWERMAN2468's Avatar
    MOWERMAN2468 Posts: 3,214, Reputation: 243
    Ultra Member
     
    #2

    Dec 23, 2007, 05:56 AM
    Yes a breaker will get hot if it has gone bad. But check to see if there are other issues causing the problem. If you are not sure, have a licensed electrician check the circuit for you.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Dec 23, 2007, 06:10 AM
    What you need to look at is the voltage across the breaker under load. It should be very small. Your assuming the breaker contacts are a short circuit. Zero resistance is unobtainable so there is always some drop across the breaker.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Dec 23, 2007, 06:41 AM
    The breaker being hot can indicate it is defective. It can also indicate that either the Line and/or Load connection is loose. Loose connection will create heat, which will then migrate into the breaker and activate the thermal trip unit inside.

    Checking the Load is simple, tighten the screw onto the wire. Checking the Line is more difficult. This is where the breaker plugs onto the busbar tab in the panel. Look for any burnt metal or discoloration of the metal tab. If it is not clean and bright, you may be able to clean it. If it is melted or distorted, the breaker needs to be moved to anther slot, and the damaged slot not used, and the panel will need to be changed.

    Measuring the voltage drop across Line and Load of the breaker is an indicator of poor contacts inside the breaker, mentioned by Kiss, and is often used as a troubleshooting method by professionals, but is impractical for a DIY'er to perform, as the voltage difference will be in Millivolts, and a meter that will measure millivolts is needed.
    Jim1954's Avatar
    Jim1954 Posts: 2, Reputation: 1
    New Member
     
    #5

    Dec 24, 2007, 08:54 AM
    Quote Originally Posted by Jim1954
    Hello,

    I have a set of common 220 breakers that are tripping, I have tested both wires with a amprobe and both wires are pulling under the limit of the breaker. I'm wondering if a breaker will get hot to the touch if it has gone bad?

    Thanks

    Jim
    Thanks for the breaker answers! I bought s new breaker yesterday and things are working fine.

    Jim

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Theory of vacuum Circuit Breaker & sf6 circuit breaker [ 15 Answers ]

I want to know about the basic Theory of vacuum Circuit Breaker & sf6 circuit breaker

Replacing GFCI Breaker With A Regular Breaker [ 1 Answers ]

I have a 15 amp circuit serving only a single outlet on my deck. It is protected by a GFCI circuit breaker in the home's single 125 amp service panel. I wish to replace the GFCI breaker with a regular 15 amp GE breaker. I will then protect the circuit with a GFCI outlet. I am familiar with...

Replacing Circuit Breaker with Higher AMP Breaker [ 8 Answers ]

Excuse me, I did look at the code book as is suggested in your Sticky. The NFPA may answer this question, but I am not knowledgeable enough to recognize it: Our offices are upstairs in an older (renovated home) building with modern wiring. We have 4 computers, 3 printers, and miscellaneous with...

New 15A breaker trips main 100A breaker [ 6 Answers ]

Hi, I've been finishing my basement and I added a few 15A breakers One room has 8 outlets in series with the first starting about 6 feet from the main panel. There is currently no load on this outlets. When installing the drywall I accidentally shorted the outlet closest to the panel. It...

Replacing a circuit breaker with a GFI breaker- q on neutrals [ 1 Answers ]

In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!


View more questions Search