Old Honeywell has the following colored wires coming out of the wall:
Green
Blue
Orange
Red
White
Yellow
I have the following terminals on the new programmable Hunter thermostat:
RH
RC
(the above have a factory-installed red jumper connecting them)
G
Y
W
What goes to what?
Thanks.
|
|
 |
Heating & Air Conditioning Expert
|
|
Dec 15, 2007, 06:56 PM
|
|
Look at the beginning of this board for the sticky notes. It is all in there for you.
|
|
 |
Ultra Member
|
|
Dec 15, 2007, 07:32 PM
|
|
Did you make a note of where the different colors were when you took them off the old thermostat? If not here is a hint for you: Look at the circuit board at the furnace and look at the terminals for the low voltage coming from the thermostat.
You will have terminals lettered as follows;
C which is the common.
G which is the control for the blower motor
W which is the control for the gas valve
Y which is the control for the outdoor AC
R which is the wire that takes the 24 volts to the thermostat.
Whatever color of wires are on these terminals must then you should connect them to the same lettered terminals on the thermostat.
Also you will have two wires connected to the furnace that are coming from the outdoor AC
One of them should connect to the Y terminal that already will have one wire on it from the thermostat, the second of the two wires should connect to the terminal marked C.
I hope this helps.
|
|
 |
Ultra Member
|
|
Dec 15, 2007, 10:36 PM
|
|
You didn`t say but sounds like you have a heatpump ,the older stat had a blue and orange wire ,you didn`t mention having a place on the new stat to hook up,, if this is true,you need a different tstat
|
|
 |
Uber Member
|
|
Dec 15, 2007, 10:45 PM
|
|
Most likely that is correct. If you aren't sure if you have a heat pump, don't feel bad. That is common enough to be covered in the sticky too.
|
|
 |
New Member
|
|
Dec 16, 2007, 07:58 AM
|
|
 Originally Posted by letmetellu
Did you make a note of where the different colors were when you took them off of the old thermostat? If not here is a hint for you: Look at the circuit board at the furnace and look at the terminals for the low voltage coming from the thermostat.
you will have terminals lettered as follows;
C which is the common.
G which is the control for the blower motor
W which is the control for the gas valve
Y which is the control for the outdoor AC
R which is the wire that takes the 24 volts to the thermostat.
Whatever color of wires are on these terminals must then you should connect them to the same lettered terminals on the thermostat.
Also you will have two wires connected to the furnace that are coming from the outdoor AC
one of them should connect to the Y terminal that already will have one wire on it from the thermostat, the second of the two wires should connect to the terminal marked C.
I hope this helps.
The different wires are still connected to the old backing plate of the Honeywell I'm replacing. I put the old front back on, and it's still operational. I'll try tracing to the furnace. And, it is a gas Westinghouse, not a heat pump. I was confused by the blue and orange wires also, since a lot of what I had found on the net said those wires often were coded for a heat pump installation. Thanks.
|
|
 |
Uber Member
|
|
Dec 16, 2007, 08:42 AM
|
|
Many thermostats will work with both heat pumps and a furnace. If you have a gas furnace, just leave the blue and orange go.
Note, I don't think they were ever common, but gas heat pumps do exist.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Wiring honeywell to hunter programmable
[ 1 Answers ]
I have an old honeywell chronotherm controller. Bought a Hunter programmable to replace it with. Question is this: Hunter has slot for Y, C, M, or O wire. Problem is, the old honeywell has a Y AND a C. All other existing wires and letters correspond, but the hunter says that Y and C which are...
New Hunter Programmable thermostat keeps blowing air
[ 14 Answers ]
Okay I'm going to admit from the beginning I have no idea about these things :o
This morning I installed the new Hunter Set & Save Programmable Thermostat (Model 44155C). It was really easy to install, the programing took a sec to figure out, and it seems to work fine except for one thing......
Wiring a hunter 44110 5-2 programmable thermostat
[ 1 Answers ]
Am trying to install a new programmable thermostat and I am having problems. My old thermostat had the following wires: white, orange, red, green yellow and blue. The new Hunter thermostat has places for RH, RC, G, Y and W. I have tried several different configurations and cannot get the a/c to...
Hunter 44110 Programmable Thermostat Wiring HELP!
[ 3 Answers ]
My current thermostat has the following six wires, hooked as follows:
Orange to O
Green to G
Yellow to Y1
Red to R
Black to C
White to W1
I am attempting to install the Hunter Programmable thermostat, which only gives me 5 placements for wires:
View more questions
Search
|