                |  | New Member |  | 
 
                  
                      Dec 14, 2007, 11:25 PM
                  
                 |  |  
  
    | 
        
        
        
       
        
        Electric Load Calculation
       
                  
        I have a Unit working at 6.5 Amps, 3 phase. I want to calculate the Power Consumption of the Unit. If I can get the formula by which the same is calculated.
 The Formula is the most important.
 
 I would be grateful, for a very quick reply.
 
 
 Regards
 
 Ujjval.
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Printers & Electronics Expert |  | 
 
                  
                      Dec 15, 2007, 04:11 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        What type of device is being used?
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Uber Member |  | 
 
                  
                      Dec 15, 2007, 07:20 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        When you say power, there are two types, true, and apparent.
 Which is that you are looking for?
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | - |  | 
 
                  
                      Mar 27, 2008, 05:31 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        The power in a three-phase system is measured in volt-amps. The formula used to calculate the power involved is:.
 Volt-amps = Sq. root of 3 x voltage (volts) x current (amperes)
 .
 Assuming you use 3 phase 110 Volts :
 .
 VA = root of 110 x 110 x 110 x 6.5 = root of 8651500 = 2941 VA
 ;)
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Guest |  | 
 
                  
                      Apr 3, 2008, 04:28 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        That is the wackiest explanation of a this formula I have ever seen.
 VA= SqRt of 3 * volts * amps
 
 VA = 1.73 * 110 * 6.5
 
 VA = 1236.95
 
 For this example.
 
 Althou, 110 volt 3 phase is very rare.
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Apr 12, 2008, 01:25 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Difference between single phase & 3 phase cable
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Jan 24, 2011, 09:29 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        what type of load resistive or capacitive or inductive to know the power factorywhich know  as pf ( cosine the angle between phase current and phase voltage = cos fi)
 the load is divided into two parts
 1- active so, power = 3*current*phase voltage*cos fi                 P
 2- inactive so, power = 3*current*phase voltage*sin fi               S
 overall power Q = Sq. root of( P^2+S^2)
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Mar 4, 2011, 09:07 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Cable size & amp calculation
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Mar 4, 2011, 09:12 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Electrical cable size & load calculation
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Mar 4, 2011, 09:15 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Cable size & load formula
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Mar 4, 2011, 09:19 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Cable size & kw formula
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Mar 4, 2011, 09:23 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Motor kw & load cable size
     |  
    |  |  
 
 
 
  
    | Question Tools | Search this Question |  
    |  |  |  
 Add your answer here.
 
Check out some similar questions!
Electric Force and Electric Field?
 [ 1 Answers ]
Hello, 
 
Can some one explain to me briefly what's the different between electric force and electric field? I am having trouble to make them clear to myself.  Thanks you so much.  
 
Jack
 
Load calculation
 [ 1 Answers ]
Hi  
 
Please advise me what are the factors considered for calculating the Tonnage Rate whilst selecting the AC units for Industry / office environment. 
 
 
Regards 
Pankaj
 View more  questions
Search
 
 |