    All of the receptacles and switches in my house are 15 Amp. I recently had a new 200 Amp breaker box installed. All of the breakers are 20 Amps for these circuits. Do I have a problem?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 11, 2007, 06:10 PM
    No, what you have is fine, no safety problem, and done often.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Dec 11, 2007, 07:35 PM
    Tk:

    What if the wiring for the 15 A outlets is not 12 AWG?



    Light switches are fine. The load never exceeds 15 A.
    Cobraguy's Avatar
    Cobraguy Posts: 140, Reputation: 11
    Junior Member
     
    #4

    Dec 12, 2007, 06:35 AM
    Quote Originally Posted by KeepItSimpleStupid
    tk:

    What if the wiring for the 15 A outlets is not 12 AWG?



    Light switches are fine. The load never exceeds 15 A.
    My first thought too. The breakers should be properly sized for the circuit wiring. What size cable are all these 20A breakers on?

    Maybe I'm assuming something I shouldn't be.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #5

    Dec 12, 2007, 07:10 AM
    Your rating of tk's answer was correct. I have rated him too recently to rate him again. If you don't have anything with a 20 amp plug on it, you don't need 20 amp outlets. The 20 amp circuits just allow you to run more things at once.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Dec 12, 2007, 05:20 PM
    I guess I am assuming the work was done properly, and am being a bit too trusting.

    Kisses point is have it checked to be sure is wise.

    It is odd to have an older panel upgraded and be able to have all #12 wire for 20 amp breakers. Were they all 20 amp fuses before?

    If this was just changed and the wrong size breakers are installed, this installer deserves to be dealt with severely.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #7

    Dec 12, 2007, 05:43 PM
    The maximum breaker size is, in part, determined by wire gage, length and service factor.

    The minimum breaker size is generally determined by the load unless the above is lower.

    Initial assumptions are #14 for 15 Amp circuits.
    #12 for 20 amp circuits

    So, if the breaker connects to #14 it should be 15 amp. If the breaker is connected to #12 wire, it can be 20 amps subject to the above rules.

    It's entirely possible that the installer got a box with pre-installed breakers.

    I'd also check if any of the breakers are GFCI and/or arc fault. Bedrooms and living rooms require arc fault. GFCI's in wet areas like outside and the bathroom and near the sink in the kitchen. These breakers require a connection to neutral, so they should be easily identified.

    Seems like a competent inspector would find it.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #8

    Dec 12, 2007, 05:50 PM
    Bedrooms only need AFCI, and not just because the panel was changed. It cannot be assumed the house wiring is such that a circuit is only for bedrooms.

    Could be minimal inspection , and inspectors usually are held harmless for what is missed.

    Length never affects branch circuit breaker size.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

50 amps vs 100 amps? [ 5 Answers ]

I recently purchased a new mobile home in Ventura, CA. The home was a "lot model" that was originally delivered from the manufacture and set up on a site, used as a model and then taken down and delivered to where I am now. The Manufacture says that it was built to run on 100 amps - it is 60...

20amp circuit breaker, 15 amp receptacles [ 2 Answers ]

I have a 20amp circuit breaker with 15 amp receptacles and light switches on #12 wire with a load of 1700, is this allowable? If not, and I change to a 15 amp circuit breaker, is the 1440 watt safety load in the code or is it a non-code safety suggestion?

Breaker Box Amps rating & Number of breakers installed [ 1 Answers ]

I have a question in regards to amps allowed in a breaker box. My breaker box has a label stating that the box has a maximum load of 200 amps, but that it is convertible. I really don't know what the convertible part means. If I look at the breakers installed, these add way more than 200 amps. ...

15 or 20 amp receptacles? [ 6 Answers ]

I had my electric service upgraded 18 years ago and had the electrician install two GFCI's, One for the bathroom and one for the kitchen. They are on separate circuits by themselves. They are each on a 20 amp breaker with 12 gauge wire and the GFCI's are rated 15 amp with 20 amp feed through. My...

Basement receptacles [ 4 Answers ]

Hi, I want to put four receptacles in my basement, its an unfinished basement and I'll put in a GFCI plug. My question is this: do I bond the metal boxes and Im not sure if I am supposed to ground the plugs that are fed off the GFCI? And I do ground the GFCI in the panel don't I? Thanks


View more questions Search