2 pole gfi breaker
I know how a single pole gfi breaker works. By measuring the difference between the current going out on the hot and coming back on the nuetral. But how does a 2 pole gfi breaker work when you hook up a hot tub and you do not use the nuetral? Is it measuring the imbalance between the two hot legs? Say if one leg was to go to ground and suddenly draw an excessive amount of current? Thank you.:p
|
|
 |
Uber Member
|
|
Nov 9, 2007, 09:57 PM
|
|
Let me ask you how you think a 2 pole breaker works when you use the neutral. That's the more complicated case.
If one leg went to ground and drew an excessive amount of current a normal breaker would trip from overcurrent. But a GFCI breaker is not a normal breaker. Name two things a GFCI breaker does. Name something it doesn't do. And we'll go from there.
|
|
 |
Uber Member
|
|
Nov 10, 2007, 05:26 PM
|
|
For some reason I didn't think you would bite.
GFCI's use transformers to add or subtract currents. When there is a difference of about 16 mA the GFCI opens the circuit. Thus a resistor smaller than R=120/16mA to ground on either leg will trip the GFCI. The GFCI also detects a grounded neutral using a different mechanism.
The 2 pole case:
We know that I(L1)+i(L2) = I(N); neutral carries difference of L1 and L2
We also know that L1 is 180 deg out of phase from L2.
So to get the difference of I(L1) and I(L2) the primary would be wound in the same direction.
Let's rearrange the eqn to read I(l1)+i(L2)+i(N) = 0
With a GFCI we want I(L1)+i(L2)+i(N) ~> 16 mA to trip the breaker.
So, we can wire the transformer primary with the currents from L1, L2 and N and check the magnatude. Anything greater tha +-16 mA will trip the 2 pole GFCI. This is why the Neutral of the GFCI has to be attached to the load side. Adding or subtracting just depends on the direction of current flow.
The special case of no neutral to a hot tub for instance just forces I(N) = 0.
Does this make sense?
|
|
 |
New Member
|
|
Nov 13, 2007, 03:50 PM
|
|
 Originally Posted by KeepItSimpleStupid
For some reason I didn't think you would bite.
GFCI's use transformers to add or subtract currents. When there is a difference of about 16 mA the GFCI opens the circuit. Thus a resistor smaller than R=120/16mA to ground on either leg will trip the GFCI. The GFCI also detects a grounded neutral using a different mechanism.
The 2 pole case:
We know that i(L1)+i(L2) = i(N); neutral carries difference of L1 and L2
We also know that L1 is 180 deg out of phase from L2.
So to get the difference of i(L1) and i(L2) the primary would be wound in the same direction.
Let's rearrange the eqn to read i(l1)+i(L2)+i(N) = 0
With a GFCI we want i(L1)+i(L2)+i(N) ~> 16 mA to trip the breaker.
So, we can wire the transformer primary with the currents from L1, L2 and N and check the magnatude. Anything greater tha +-16 mA will trip the 2 pole GFCI. This is why the Neutral of the GFCI has to be attached to the load side. Adding or subtracting just depends on the direction of current flow.
The special case of no neutral to a hot tub for instance just forces i(N) = 0.
Does this make sense?
Yes it makes sense. The reason I didn't BITE as you called it is I have been away from my computer for several days. I have been through the IBEW's apprenticship program and have been an electrician for almost 17 years. If I wanted to be TALKED DOWN TO I would go see the electrical engineers on site and have a conversation with them. They always know how to make it work on paper but us guys in the field are the one who have to make it functional in the field. You sound just like one of them. I was looking for an intelligent answer from someone who knows, not a talking to from some a-hole who has to act like he is god's gift to elecrticity. In the future if you would like to talk down to people, go do it somewhere else!!
|
|
 |
Uber Member
|
|
Nov 13, 2007, 05:00 PM
|
|
Burrhead:
Sorry if I offended. I have been diagnosed with psycological issues which might cause these kind of problems. I'm even glad that you understood the explanation. Sometimes I have trouble there as well. Not having any idea of the background of a person makes it harder to come up with an explanation. Do you have any other questions?
KISS
|
|
 |
Uber Member
|
|
Nov 14, 2007, 05:17 PM
|
|
Just to speak on Kiss's behalf, I am sure he sincerely did not mean any offense. I did understand where he was coming from with his technique, just a bit rough around the edges.
I am glad your in the trade thou, it helped you understand the answer.
If you were a layperson, your eyeballs would be spinning.
He is working on his answers to keep in step with his name.
I do need to ask where the 16 amps comes from. All GFI devices for personnel protection are set for 5 Milliamps difference.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
How does a 2 pole gfi breaker work
[ 18 Answers ]
I have a hot tub requiring a 240v circuit but it has a factory 3 wire plug on it. I put in a 2 pole gfi breaker and ran a 10-3 to the tub. Problem is there isn't any where for the neutral on a 3 wire 240v receptacle. It's my understanding that you must have a neutral for the gfi to operate properly...
Two Single Pole GFI's = one Double Pole 220v GFI?
[ 6 Answers ]
Hello there,
Installing a pool motor, 220v hayward northstar two speed. Could not find a double pole 40 amp GFI, electric supply store recommended two single pole 20A GFI's sharing a neutral? Does this make sense. I have a 40amp double pole in the main feeding the sub via the sub panel...
Testing Dual Pole 50x2 GFI Breaker
[ 2 Answers ]
I have a dual pole screw-in Cuttler Hammer breaker with ground fault interrupter, the connected poles have 50 amps each. The breaker is used to connect to a hot tub. I'd like to know if the breaker is okay.
I've tested and found current on the IN side, with none on OUT, with the switch...
One pole of untied double-pole circuit breaker breaks
[ 5 Answers ]
I recently purchased a new dryer (220 v appliance) to replace an older model. The old dryer was connected to the panel via a double-pole breaker except that there was no clip or tie between the poles. I changed the location of the outlet when installing the new dryer, replacing the cable with the...
Replacing a circuit breaker with a GFI breaker- q on neutrals
[ 1 Answers ]
In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!
View more questions
Search
|